new crown gas fired steam boilers - water needed every week

redheadgenes
redheadgenes Member Posts: 24
edited December 18 in Strictly Steam

Hi heating help!

I have tried to do a bit of research on this issue on this website (haven't yet read the book) but posting because existing posts/answers all have slightly different scenarios, and I'm looking for a second opinion.

I bought a 3 family in new england in july. The house had two gas-fired steam smith boilers from the early 70s that both had to be replaced (each required repairs ($-$ range) to make them work for this season, I was advised by 4 separate plumbers to replace). Each heats one apartment. (third apartment is electric baseboard).

I replaced (after another saga with repiping one of them that might be relevant) with a steam guy who — after reading this website — I asked some questions of and he seemed to know his stuff. For example he measured the radiators and ensured fit unlike the other plumbers I contacted for a quote, yet was still in the standard rather than steam specialist price range (which was in the region of $ more total).

Prior to replacement, both boilers needed refilling apparently once a week or so during peak heating season — which seems like too much. i thought replacement would fix that.

Boiler 1 was installed in august, and has been on since Novemberish - I've had to fill it once.

Boiler 2 was installed early dec (10 days ago) has needed refilling already.

Vents on the boilers were not changed - should i have that done? I had two new vents installed on radiators in boiler 1 apartment because they were heating as well after boiler replacement. We'll see how those do.

No obvious leaks near the boiler or on any of the radiators or out of the chimney (chimneys are also all plugged with insulation material and not in use).

One radiator in boiler 2 apt has always "made a loud clanging sound." So I could have that vent changed.

The other thing to note: before replacing, I had boiler 2 repiped which worked for about a month. immediately after the repiping job, there was an issue where the pipes weren't connected enough and steam was clearly escaping from the pipes immediately around the boiler. I have a video. This was immediately fixed, then the boiler worked fine for about a month or so. then, there was some problem that developed with the mechanism (sorry i don't know the term) that connects gas to pilot, so the pilot was lit but the boiler wouldn't fire. my understanding is that the prior owner of the house had done small fixes every year for several years. this was an $ fix, i opted to replace the boiler as I had been told to do that initially. my plumber did it without charging me again for the piping.

Pictures in comments. how does the piping look ok? I know insulation needs to be put on. is that part of it?

plumber suggested I have all the vents changed (on the boiler and in the two apts) to fix the water loss problem. does that sound right?

again, no obvious leaks although i see in other posts that leaks can be in places you can't access. plumber said we would notice a leak, especially since boiler 2 (which seems to have the worst water loss problem) is connected to the ground floor apartment, so the leak would be visible in the basement or basement ceiling.

any thoughts are appreciated, let me know if more info needed. should i have another plumber come out?

«1

Comments

  • redheadgenes
    redheadgenes Member Posts: 24
    edited December 17

    BOILER 2 (with most water loss)

  • redheadgenes
    redheadgenes Member Posts: 24

    Boiler 1

  • Dan_NJ
    Dan_NJ Member Posts: 260

    FYI Pricing is not mentioned on the site - dollar amounts are not discussed, you need to edit that stuff out above

  • Jamie Hall
    Jamie Hall Member Posts: 24,988

    The amount of water you are adding is not acceptable. So the question is — where is it going?

    It is not impossible for a new boiler to leak, although those are small enough that they were likely delivered in one piece (I am puzzled by the remark about the chimney — is it in use? In one place you say something about it being full of insulation?)

    It is possible that some — though likely not all — of the water loss is from the vents. Some of it also may be from the shutoff valves on the radiators. Those all need to be checked and maintained (or in the case of the vents, replaced) as needed. Most of it, though, is likely to be from plain vanilla leaks in the piping. There is, though, a definite and useful sequence to finding leaks — but it pretty well needs to be done in warmer weather!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,526
    edited December 17

    I think prices are vague enough. $1800 to $2000 for general repairs led me to choose replacement over repair. It is not like he is saying that part number XYZ is being replaced for the price of $1830.59 including labor.

    As far as the water problem: Thare are three places the water can go:

    1. If the boiler has a leak above the water line, then steam could be leaving out the vent along with the flue gas. You may never see water on the floor if that is the case.
    2. If the steam is leaking at the packing nuts, air vents or cracked pipe or fitting, that should be easier to find. it will be steam so you may not see water on the floor, but that steam will condense when it hits the cooler atmosphere outside of the stema pipes and radiators. that condensation may show up as water on cold windows, or it may show up as rotted wood near the source of the leak. There may be more than one of these.
    3. The hardest one is a leaking wet return pipe that is below the floor. Sometimes return pipes need to go past walkways and doorways. These pipes are often piped below the floor. If you have a wet return below the floor, you need to start to dig up the floor in a few locations to find the leak. If that is a big project, then you can cut the wet return at either end of the pipe where it exits (and enters) the floor, cap it off, then pressure test it. 


    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks ed! I will take out my prices if nesc, but seems there is some disagreement

    1. If the boiler has a leak above the water line, then steam could be leaving out the vent along with the flue gas. You may never see water on the floor if that is the case.

    This is fixed by replacing the vent on the boiler itself?

    2. If the steam is leaking at the packing nuts, air vents or cracked pipe or fitting, that should be easier to find. it will be steam so you may not see water on the floor, but that steam will condense when it hits the cooler atmosphere outside of the stema pipes and radiators. that condensation may show up as water on cold windows, or it may show up as rotted wood near the source of the leak. There may be more than one of these.

    So I should look for condensation or evidence of water around radiators and around the boiler itself? And then the fix is: addressing the packing nuts, air vents or cracked pipe or fitting.

    3 The hardest one is a leaking wet return pipe that is below the floor. Sometimes return pipes need to go past walkways and doorways. These pipes are often piped below the floor. If you have a wet return below the floor, you need to start to dig up the floor in a few locations to find the leak. If that is a big project, then you can cut the wet return at either end of the pipe where it exits (and enters) the floor, cap it off, then pressure test it. 

    its a dirt floor basement - there isn't any piping below the floor. so i should look for condensation and/or leaking along the wet return pipe, which is this case would be one above the boiler..

    How does the pipe job look to you? many thanks

  • Jamie Hall
    Jamie Hall Member Posts: 24,988

    1 —- no. @EdTheHeaterMan wasn't referring to a steam vent, but to the exhaust from the boiler burner up the chimney.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    redheadgenes
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,526
    edited December 18

    Let me re-word this "

    1. If the boiler has a leak above the water line, then steam could be leaving out the vent along with the flue gas. You may never see water on the floor if that is the case.

    1. If the boiler has a leak above the water line, then steam could be leaving out between the cast iron sections. That steam will then go up the chimney vent along with the byproducts of the combustion process. You may never see water on the floor if that is the case. (steam will go up the chimney as steam not water)

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    redheadgenes
  • ethicalpaul
    ethicalpaul Member Posts: 6,815
    edited December 18

    It's almost certainly leaking vents (radiator and/or main) and/or radiator valves. There is a much less likely chance that some radiator runout or section of main is leaking, but it's possible. It could be a wet return, especially if any of them are buried where you won't see the water.

    Even a non-obvious leak could let out a gallon or so per day, and for those boilers, a gallon of condensate might be 1/2" to 1" of height on the gauge glass.

    There's almost a zero chance that either boiler itself is leaking IMO

    Edit: sorry everyone when I posted it wasn't showing me those earlier responses so I may have repeated what others said, I have to go back and look!

    Edit 2: Yeah i was confused by that comment about the chimneys being plugged up and unused too!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    redheadgenes
  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks ethicalpaul!

    OK I think I don't understand how my chimneys are working, the fireplaces are non-operational, apologies I'm such a newbie to … everything!

    I will check everything again for leaks - all the valves and all the vents. The problem so far is that I have looked at all 16 radiator valves/vents and the valves/vents on the boiler and i just do not see condensate or any kind of leaking or extra misting. this plumber did not see anything either but he did suggest replacing all the radiator vents in boiler 2's apt (that boiler is losing more water). before i paid for that i wanted to get a second opinion, so here i am…

    Do you suggest having a qualified person test all the valves / vents or is this something i could do myself after reading the manual? or is there an element of technique there where i should not attempt..the guys who replaced two valves on radiators in my apartment did so in about 30 seconds. after replacing both boilers i just am frustrated at having further elements to fix and pay for.

    Thanks for your help and time

  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    Well they should have put checking/replacing any bad vents in their boiler install quote, are you sure they didn't?

    To see if vents are working, you set up a long call for heat, like make the system have to gain like 5 degrees. Then you run around to all the radiators to see if they are filling with steam. That tells you the vent is letting air out like it should.

    Then you keep running around to all the radiators until they start to completely fill up with steam all the way to the vent. When steam gets to a vent and makes it "steam hot" the vent should close and not allow any steam to escape. You can hold a spoon in front of the little hole in the vent to see if it's letting out steam.

    Also check the valve (note the difference between a steam vent, and the radiator's valve that has a handle on it) to see if it is leaking, hissing, or dripping.

    You don't want to see any hissing, fogging of the spoon, or dripping anywhere because you should only be having to add like a gallon per month to these boilers.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    redheadgenes
  • AdmiralYoda
    AdmiralYoda Member Posts: 686

    Small steam leaks add up fast! I had a leak in between two sections of one of my radiators. It didn't leak enough to drip, it was at the top of the push nipple on the bottom of the radiator but it would bubble a bit.

    For the longest time I dismissed it because I thought it was too minor to make a difference….all the while I was adding make up water weekly. I fixed that leak and guess what…I top the boiler off once a month maybe.

    Set the thermostat up high to get the system full of steam and a little pressure. Use a small mirror and move it around all the joints, valves, vents, etc. You will see little wisps of fog on the glass of the mirror if steam is leaking. Sometimes leaks are so minor you can't see or hear them….but they are there.

    bburdredheadgenes
  • Jamie Hall
    Jamie Hall Member Posts: 24,988

    As I have been heard to say… one drip every 10 seconds is a gallon a day.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossvethicalpaulredheadgenesSuperTech
  • delcrossv
    delcrossv Member Posts: 1,437
    edited December 18

    3 bad radiator vents and a slow valve leak (needed a mirror to see it) added up to a weekly refill on a fairly large multifamily system.

    Chase down those leaks!

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    ethicalpaul
  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks to all!

    Re: ethical paul: — Well they should have put checking/replacing any bad vents in their boiler install quote, are you sure they didn't?—

    They didn't - and they charged me to change out two radiator vents. I'm sure if I check the boilers themselves and find leaking (on the boiler vents / valves) they'll come back and do that. But it seems like they view radiator work as a separate charge. I'm not sure what to think about that - the other 2 quotes I got were similar and only included: cost of boiler, cost to install boiler. The larger quote I received (significantly higher) included vent work on the radiators themselves.

    Looking again at their boiler install quote it explicitly excludes "Repair or replacement of existing radiator vents + valves."

    At the same time it includes:

    "We hereby state that the work we have proposed will correct the problems associated with the improperly piped boiler and that all of the radiators will heat thoroughly and evenly, the boiler not lose water abnormally, the boiler water will stop surging and the boiler will stop short cycling. In the event that the work we complete does not improve the situation then all monies paid for our work shall be refunded in full."

    What do people think about this? Does it seem fair? I guess the no radiator work was in the quote…

    I will look at the boiler vents with a mirror and get them to come back if I find any misting or fogging.

    I will follow @ethicalpaul @delcrossv and @AdmiralYoda advice and chase down mirror fogging in the radiators (at valve and vent). Are these two parts relatively possible to replace yourself? Or should I call back a professional?

  • delcrossv
    delcrossv Member Posts: 1,437
    edited December 18

    Valves are easy

    If valve is leaking at the valve stem :

    First, try tightening the top (packing) nut 1/4 turn. That's usually enough.

    If it's still leaking, turn boiler off, remove the packing nut and use a pick , like a nut pick or dentist's pick to remove the old packing; get some new thin valve packing at the hardware store and wrap around the valve stem while stuffing it gently onto the gap where the old packing was. when you get to 1/16 or so over the top replace the packing nut and SLIGHTLY tighten. If you can't turn the handle you tightened it too much. If it's still leaking, tighten a little more.

    Vents unscrew. Again Boiler off, unscrew old vent, put some teflon thread tape on new vent(be careful not to occlude the port) and screw in. Vent should be vertical- only hand tighten these.

    Maid -o-mist and Gorton are decent rad vents. Get them at Supplyhouse.com- NOT your local Home Depot.

    The red circle is your main vent

    This should be removed and the pipe replaced with a 3/4 street elbow to at least an 8" nipple. Put a Gorton #1 main vent on the end. Your installer should do that for a reasonable fee.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    ethicalpaulredheadgenesexqheat
  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    If they excluded it in their quote, then it was fair.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    delcrossvredheadgenes
  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks so much this is all soooo helpful!!

    @delcrossv this is amazing, thank you. Do you think I should have the main vent on the boiler replaced regardless or only if (after doing the mirror technique while the boiler is firing up 5/10 degrees) I notice fogging, misting, etc?

    I'm going to get Holohan's books. I think those should have end of season tips - like what you should do at the end of the season to keep your system running well. I've heard cleaning off the boilers can help. Let me know if you have any tips! i'm so grateful for all your help

  • delcrossv
    delcrossv Member Posts: 1,437

    Two separate things. Leak checking to drop water usage AND redoing the main vent because how it's installed now guarantees poor performance and early failure. 🙂

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks @delcrossv !!

    You originally said: This should be removed and the pipe replaced with a 3/4 street elbow to at least an 8" nipple. Put a Gorton #1 main vent on the end. Your installer should do that for a reasonable fee.

    This boiler was installed in August. Shouldn't the plumber who did that work come and correct it for free? His labor is "guaranteed for a year" as per the quote. Is there a reason there would be another fee for this? What do you think is fair? Piping around the boiler was done at the time of install, was included in the quote.

    And you think that the 3/4 street elbow to at least a 8" nipple is contributing to poor performance / water loss?

    I am really regretting the fact that I didn't read the book before hiring someone to install these boilers. Huge mistake.

    What do you think about the vent on boiler 2? (first post with pictures)

    And do you see any other issues with the piping around these boilers? It seems like, since this is "guaranteed for a year" I should be able to get mistakes fixed without additional payment.

    Thank you so much

  • redheadgenes
    redheadgenes Member Posts: 24

    The other thing is that members of the master plumber's team came to "skim the boilers" last week - this took them all of 1 hour. Based on the book, they didn't really do it but I also wasn't charged for this. I don't know if skimming is usually included with install and how to check this was done sufficiently. Boiler 1 has some floaty sludge in the sight glass. For this, I might hire another plumber next year to skim properly, but let me know emergency things to look out for that indicate I should do it immediately. "Skimming" was part of the quote for the boilers install but seems to have just involved two younger guys draining the boiler a bit. Although I didn't watch them work. Many thanks

  • delcrossv
    delcrossv Member Posts: 1,437
    edited December 19

    Should do the same on Boiler 2.

    I don't have your contact in front of me, and wouldn't comment if I did, but it seems that most installers (with some notable exceptions) do not include vent replacements with boiler installs. 🫤

    You should mirror check both main vents. If they're leaking then, yes they're contributing to your water loss.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • redheadgenes
    redheadgenes Member Posts: 24

    And also @delcrossv @ethicalpaul

    Is it appropriate to ask this plumber to install a Mud leg and a “shutoff and a drain valve in the main wet return line, just before it connects to the Hartford Loop" if this was not initially done? Again this work is supposed to be guaranteed for a year, and I should have asked for those things up front. I imagine asking to reinstall the main vent should be included in warranty bc it's done wrong, but maybe these elements need further payment.

  • delcrossv
    delcrossv Member Posts: 1,437

    Drain on wet return? It's there.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 6,815
    edited December 19

    the steam piping and return look pretty ok. Skimming is not draining and yes your gauge glass shows signs of oil requiring skimming.

    The makeup water piping is a horror show but that won’t affect your boiler’s performance

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    redheadgenes
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,526
    edited December 19

    Did you start out with the statement that your boiler needs water weekly. I would think that your boiler is "losing water abnormally".

    And your contract says "We hereby state that the work we have proposed will correct the problems associated with the improperly piped boiler and that all of the radiators will heat thoroughly and evenly, the boiler not lose water abnormally, the boiler water will stop surging and the boiler will stop short cycling. In the event that the work we complete does not improve the situation then all monies paid for our work shall be refunded in full."

    Based on that line in the contract, I think you need to apply for the "refund in full" in writing. See how fast they start looking for that leak.

    Start keeping a written log of how much water you are adding and how often.

    In order to know how much water you are adding, you can mark the water line with tape on the gauge glass. Then mark the spot where the LWCO stops the burner by removing that much water into a bucket. From the bucket, measure how many quarts or gallons that much water is on the gauge glass. (For example 1.5" on gauge glass = 2.7 gallons or something like that)

    Now every time you need to add water you know how many gallons you are adding and you can write it down with the date and keep a record of it.  

    That info will hold up in court if that boiler is still losing water in 3 years when it gets to court.

    But it won't get that far. I had the same thing happen on a church that used 999 gallons of water in the first 6 weeks of operation. I found a buried wet return in a crawlspace that was rotted away. All the return condensate from that section of the building was draining into the crawl space under the sand. The church agreed to pay extra for that pipe repair. And that repair solved the boiler water loss problem.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    redheadgenesGrallert
  • redheadgenes
    redheadgenes Member Posts: 24
    edited December 19

    Hi again @ethicalpaul

    looking at my quote for boiler one, I think they did replace the main vent. See below for how it's listed in my quote:

    Unless the thing you're referring to - that should be replaced with a Gordon #1 main vent — is something else.
    Also reading the steam book now, I accepted copper for the supply pipe, which I should not have done. or maybe "Copper Type L" doesn't corrode in the way copper tubing does.

    Does the makeup water piping look professional at all? If you had paid for it would you complain? I guess it does not impact performance

    MATERIALS

    (1) Crown BSI SERIES - BERMUDA , gas fired steam boiler*

    (all) All steam piping shall be Schedule 40 steel pipe and fittings.

    (1) Hoffman main steam air vent

    (all) Copper Type L for water supply pipe

    (all) Wire and electrical controls

    (1) 120V firo-matic safety switch

    (all) Parts, pipe, fittings, valves, controls or other required materials are included for work described herein.

  • TKPK
    TKPK Member Posts: 55

    I think those statements were from the higher quote that he did not accept. The higher quote was comprehensive and guaranteed including vents, traps and valves.

    Incredible how pricey something as simple as a steam trap cartridge is for B to C.

  • redheadgenes
    redheadgenes Member Posts: 24

    Thank you! where would I find if a "Mud leg" has been installed for later draining?

  • redheadgenes
    redheadgenes Member Posts: 24

    No that was the language from the quote for repiping boiler 2. I accepted and paid for that quote. Before I replaced it, the original 1971 boiler was repiped — multiple plumbers told me the piping job was bad — but then another issue with the boiler occured (ofc as soon as heating season began) and I had to have the boiler replaced. This plumber agreed to install the boiler without charging me for piping it again. So I think this language should apply - this boiler's system was having a water loss problem before I replaced the boiler. I replaced the boiler (and the piping outfit along with it) and it's still having water loss. Seems like this quote should apply.

    What does this mean:

    Incredible how pricey something as simple as a steam trap cartridge is for B to C.


  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    I wouldn’t focus on this. You have a tiny wet return with a drain. It’s fine. At least on one of your boilers. This is a very confusing thread

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    delcrossv
  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    Also reading the steam book now, I accepted copper for the supply pipe, which I should not have done. or maybe "Copper Type L" doesn't corrode in the way copper tubing does. 

    I don’t know what you are referring to. If you mean the makeup water supply, copper is fine. Steam pipes should be steel and yours are



    > Does the makeup water piping look professional at all? If you had paid for it would you complain? I guess it does not impact performance

    No, it’s garbage. Look how it’s all just swinging loose. But pick your battles. Were these installs inspected?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    Hi again @ethicalpaul

    looking at my quote for boiler one, I think they did replace the main vent. See below for how it's listed in my quote:

    Boiler 1’s main vent is insufficient as was pointed out by another poster. It’s that skinny chrome one near the ceiling. I don’t think I’ve seen boiler 2’s

    Why you listed boiler 2’s pictures first and labeled them each at the bottom will haunt me to my dying day

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • delcrossv
    delcrossv Member Posts: 1,437

    Boiler 1’s main vent is insufficient as was pointed out by another poster. It’s that skinny chrome one near the ceiling. I don’t think I’ve seen boiler 2’s

    It's in the pictures, same thing: just stuck on the end of a reducing tee.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    ethicalpaul
  • TKPK
    TKPK Member Posts: 55

    sorry, I misunderstood about which quote was which.

    My last comment was about how costly it is for a consumer to buy components from a supply house. Policy is we don’t mention pricing but this is catalog price right off the web so I think it’s ok … I’ll keep it general anyway

    Replacing main vents are 40-140 apiece depending on model/capacity … I needed 7, split between the two prices.

    Steam trap cartridges for my simple model are 70/apiece. I have 21 radiators.

    Last time I replaced everything was about 15 years ago and my neighbor was a commercial mechanical systems distributor and I was able to buy everything from him for a very small fraction … to the point I told him to at least charge me his cost. He said he was still making money on the parts. Unfortunately he has passed and the family sold the business.

    If I were to replace all of my traps, valves and vents on my system it would cost more than I paid for my boiler including install.

    When a contractor takes system responsibility when he installs a new boiler it is not a trivial thing. It can sound like a boiler plate throw in but it could cost the consumer several thousand dollars to replace all those components and considerably more if he had a contractor do it. It would be interesting to know the delta % from a guy just doing the purchase, demo, install and near boiler piping and another guy taking system responsibility with full money back guarantee … that is honestly pretty incredible and way more professional than I usually find these days. I’m sure it is a big premium.

    B to C is business to consumer, wish I could have at least gotten B2B prices for all the stuff I have bought to fix my system this year. Payback might be 2-3 years but maybe my boiler will last another 10 years?!? BTW I kept all the old cartridges from 15 years ago and just plumbed an easy way to test them and they were 100% good.

  • ethicalpaul
    ethicalpaul Member Posts: 6,815
    edited December 19

    Ahh there it is on boiler #2. I thought I saw up there that one of the installers said they were putting on a Hoffman main vent which neither of these is. Not that I like Hoffman main vents, but these ones look bad:


    > Hi again @ethicalpaul

    looking at my quote for boiler one, I think they did replace the main vent. See below for how it's listed in my quote:

    OK so if it says they should replace it on the quote, see if there are any shiny new main vents on your main pipes near the basement ceilings. In the photo above it sure looks like a crappy old vent

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    delcrossv
  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks @ethicalpaul

    I am sorry the thread got so crazy. Next time I will put the image description first.

    This is all really helpful. My quote definitely says Hoffman main steam air vent

    Since we think these are not even Hoffmans, I will ask that they replace with Gorton #1 main vent.

    Final question - I understand in general radiator work is not included with these quotes, and its not included in my quote. However, their contract says I get a refund if the repiping doesn't fix the problem (including water loss). Do you think it's reasonable for me to expect them to fix the main vents? Is there anything else you'd suggest I ask them to do to make the boilers perform better? As all the surrounding piping, vents etc, are included in their labor warranty.

    As you suggested, I'll work on the radiators myself. But want to get the most out of my contract with this plumber. Thanks

  • ethicalpaul
    ethicalpaul Member Posts: 6,815

    Your question confuses me a little because if they promised in their quote to replace the main vent and they didn't, it doesn't seem like you should have to worry about them fixing the main vents, they should have replaced them and you should be able to ask them if they did.

    I think I know that you have two different installers with two different contracts, but you get what I'm saying I hope.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • redheadgenes
    redheadgenes Member Posts: 24

    Thanks @ethicalpaul

    it's a confusing scenario, but thanks. boiler #2's vent is just old, clearly unacceptable. Thanks for pointing that out. Boiler #1's incorrect vent looks like it was newly installed but you're saying that it's insufficient, even if it is the Hoffman vent they had promised. What I am expecting this plumber to say is — "we installed a new Hoffman vent, as we said we would in the quote you agreed to, what is the problem?" And I'm going to say: it isinsufficient, please replace with "a 3/4 street elbow to at least an 8" nipple. Put a Gorton #1 main vent on the end."

    And I'll say that it's insufficient and therefore potentially contributing to the water loss issue. Can you give me a bit more info about why boiler #1's valve is insufficient that I can use in my argument with them?

    The problem is I'm going to have to argue with them, and they know I don't know much. Many thanks

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,526

    @redheadgenes

    I am trying to follow this conversation and want to clarify some of the things stated here.

    1. Please disregard any contracts or referenced from plumbers you did no pay or have any contract with, in order to eliminate confusion.
    2. A professional tradesman gave you a price for repiping your old boiler and you paid for that work
    3. The same professional tradesman then installed a new boiler on the same system that the previous repiping was completed.
    4. The contract for the repiping made the statement "Loosing water abnormally" … and … "refund in full" in the terms of the agreement.

    Are statements 2, 3, and 4 above correct?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?