Sq ft of steam:sq ft of EDR
2»
  • ChrisJ
    ChrisJ Member Posts: 17,350
    No, but it's never too late to improve so keep trying.
    delcrossvLRCCBJethicalpaul
  • AndythePlumber
    AndythePlumber Member Posts: 76
    edited December 2024
    I just want to thank everyone for their input and knowledge. The question-at least to me-has been handsomely answered. The church I’m quoting measures at 970 sq ft edr. We have a hybrid system
    One pipe on the first/second floor radiators, and the basement has 2 pipe baseboard. The baseboard we have deduced was added to the system and while doing so destroyed the a dimension, necessitating a feed pump. We are going to abandon the baseboard. This will take it back to a true one pipe gravity system. Mooting that pump. Simplify all that happy crappy. Then we are going to install a hot water boiler for the baseboard. Two separate-simpler systems.
    970sq ft edr.—current boiler has 2700sq ft steam rating. We can do much better. The previous contractor clearly used the “door” method for sizing
    Thanks all
    THINK
    delcrossv
    ethicalpaul Member Posts: 8,741
    You can easily run hot water from the steam boiler through the baseboard
    delcrossvLRCCBJ
    Peerless 64-08. And it will have enough left over to run your hot water loop and the tappings to make it super easy
    AndythePlumber
  • saias
    saias Member Posts: 20
    I've been trying to understand this. For something that seems like simple math, I find the available information to be confusing/misleading. If I'm reading things correctly from the Peerless specs, the steam sq ft rating includes the 1.33 pickup factor.
    "Steam ratings are based on a piping and pickup factor of 1.33."
    I get there are good arguments for and against 1.33, but I don't want to get into that debate.
    So, is the 996 sq ft rating on the 64-08 actually 749 sq ft when you take out the pickup factor?
    My EDR is 332 sq ft, but a radiator was removed at some point by a previous owner that I would like to reinstall. This will likely take the system to 360 sq ft. Would the Peerless 63-04L rated at 383 sq ft be ok? My current boiler is rated at 479 sq ft.
    Yes it would be plenty
    No, the opposite. The boiler is actually larger than that rating
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    Paul posted an excellent chart for the Peerless 64 above.
    Take a look at "gross output" for the 64-08. You will see 318 for steam. This is the output after the combustion efficiency is included in the data. You lose 81 KBTU out the chimney.
    Now look at the "net ratings" for steam. You will see 239. The manufacturer assumes that you will need 33% additional capacity so they rate the boiler at only 239 KBTU despite the fact that its output is actually 318. The 33% reduction has been a bone of contention around here for years.
    If it were me, I'd use the 63-03. 98 KBTU yields 408 sq ft. You'd have a pickup factor of 48 sq.ft (360 EDR)…………..12%. Plenty if you insulate the piping and install it per the manual. It will never cycle on pressure.
    ChrisJethicalpauldelcrossvsaias
  • saias
    That seems counter to what Peerless and other manufacturers say on the spec sheets. Maybe it's just poorly worded. The Peerless footnote ("Steam ratings are based on a piping and pickup factor of 1.33") is not clear. If what you say is true, why don't they say something like "Steam ratings are based on the connected radiator EDR and does not account for any pickup factor."? Not a question for you, but for Peerless marketing.
  • KC_Jones
    KC_Jones Member Posts: 5,933
    Your statement makes no sense. The boiler rating in sq ft accounts for the pickup factor. So adding in:
    "Steam ratings are based on the connected radiator EDR and does not account for any pickup factor." would be a factually incorrect statement.
    2014 Weil Mclain EG-40
    ethicalpaulLRCCBJ
    Yeah I think the existing wording is fine, but regardless, this is why it's just good to look at net sq ft of steam vs EDR, so you don't have to be confused by all this net/gross btu stuff. Allow them to make things easy for you.
  • ChrisJ
    Personally, I look at the gross output spec and do my own math.
    For most who are confused by this stuff, I'd say go by the steam EDR spec of the boiler and don't add anything to your number and try to get the boiler number as close to the radiation as possible. Preferably being slightly under on the boiler side. If the boiler says it can do 325sqft and you've got 300-350 I'd call that good. If the boiler says it'll do 325 and you've got 250, even 280 I'd say no dice, go down a size.
    ethicalpaulLRCCBJdabrakemansaias
  • LRCCBJ
    "Steam ratings are based on a piping and pickup factor of 1.33, so we divided our net output by 1.33 to reflect this reduction in the capability of the boiler"
    Feel better now?😀
    I'll let Peerless know. I'm sure they will change it instantly.
    saias
  • dabrakeman
    dabrakeman Member Posts: 1,001
    Having spent my entire career sizing systems, not steam heating systems but rather automotive braking systems I think Jamie's statement :
    "And of course that is the least predictable variable of the whole lot! What are the expectations of the end user?"
    ,hits the nail on the head. A home or business HVAC system is like a brake system, a safety system first and foremost. Therefore, rules have been developed for the near worst case user/application. You as the designer do not know whether the end user is Mario Andretti living at the top of a mountain or granny living in Nebraska. Maybe the next owner of that old house is also granny who needs the home at 80F and doesn't have the money or wherewithal to fix all those leaks and drafts in the house. Certainly the advantage of heating is that each application does have the opportunity for individual evaluation and in most cases the "rules" can be bent quite drastically, however, not convinced that is justification to change the rules defining the starting point though.
  • ChrisJ
    Minor issues in a braking system like a balancing problem could kill people. I might even say are likely to kill people. Airplanes are a similar situation, minor problems could kill.
    As long as a few radiators heat in a home, usually it won't have a life and death situation, no?
    I think braking systems in vehicles are far more critical. I'd also like to talk to you about them in PM if you ever have time.
  • dabrakeman
    Happy to
    Jamie Hall Member Posts: 27,318
    Hmmm. Well, I agree that adequate (or better!) braking systems in a vehicle are a more obvious problem. However, as our friends the Brits across the pond are finding out the hard way, inadequate heating systems — or the inability to pay for heat — do, in fact, kill people. The current flap is over a fuel subsidy, and there is a rumbling ongoing roar over forced conversion to heat pumps, but the figure buried in the uproar is that inadequate heat for whatever reason is a factor, and sometimes the only factor, behind excess death rates among older people of around 10% (that is to say, around 10% of the over 80s who die in any given year probably wouldn't have, had they had adequate heat). Something to ponder.
    delcrossv
  • saias
    That's what I thought, but I was thrown off by Paul's response that the boiler is larger than the rating.
    I had in my head to size the EDR as close to my radiator sq ft calculation and go slightly under if possible just as ChrisJ said.
    Appreciate the responses to my overthinking this.
  • ChrisJ
    Overthinking it is much better than not thinking about it.
    It's best to get it right.
  • ChrisJ
    Not being able to pay for heat is very different from what would happen if a steam boiler was slightly undersized, or even grossly undersized, no?
    I'm thinking of all of the houses that have been heated by a single woodstove for centuries.
    Isn't it? I'm referring to the boiler's Net Sq. Feet of Steam rating
    AndythePlumber
  • KC_Jones
    Maybe if we show all the math for the 63-08 it will make sense to everyone. So the gross output of the boiler (318000) is higher than the actual rating they give to it (239000). The actual rating is what is matched up to the radiation square footage (996).
    Input
    399000
    Efficiency
    80%
    Gross Output
    318000
    Pickup
    33%
    Net Output
    239000
    Net Output SQFT
    996
    Pickup
    79000
    Pickup SQFT
    329
    saias
  • delcrossv
    delcrossv Member Posts: 2,203
    So, to put an end to the confusion, sizing to listed sq.ft. will INCLUDE a 33% pickup?
  • ChrisJ
    Every boiler manufacturer's STEAM EDR/SQFT spec includes the 33%.
    If it says it's good for 300SQFT, that includes the 33%. If you want to go by the book, if you have 300sqft, you find a boiler that says 300sqft.
    delcrossv
  • saias
    My takeaway is the listed sq ft accounts for the 33%. The number does not actually include the 33% which is why you can match the boiler sq ft to your actual sq ft.
    He said "sizing to listed sq ft will include…" not that the number includes it. We are really splitting hairs here.
    delcrossvsaias
    What is it Eliza Doolittle sang? "Words! words! I'm so sick of words! I get words all day through…"
    It's entirely a matter of clearly understanding the definitions of the various terms… and using them consistently.
    LRCCBJneilc