Temp drops to 55 at night

lab
lab Member Posts: 3

although my forced air gas furnace keeps the temp I set, 68°, 24/7, it drops to 55° at night. The furnace feels warm, so I thought maybe the fan wasn’t working. I set the thermostat to the fan staying on and it worked, but the temp didn’t go up.
Can anyone help?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • hot_rod
    hot_rod Member Posts: 25,168

    filters clean? Did it work years past?
    Keep the thermostat in the heat mode.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • lab
    lab Member Posts: 3

    yes it worked in the past and until a couple nights ago. Blower fuse was replaced about 6 months ago; Other than that, no issues. Thermostat is in heat mode -

  • Jamie Hall
    Jamie Hall Member Posts: 26,072

    Do you have a setback on the thermostat?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • worldclasshvac
    worldclasshvac Member Posts: 40

    Ita likely tripping a limit and shutting down prematurely. Very common issue and the fix depends on what furnace is there. Post the model #. Could also be weak inducer causing pressure switch to flutter

  • lab
    lab Member Posts: 3

    thank you all. I had a friend check it because it quit completely, and it’s a relay. Won’t be here til Monday, but it’s a $4.50 part.

    PC7060

Welcome

It looks like you're new here. Sign in or register to get started.

Welcome

It looks like you're new here. Sign in or register to get started.