Hey all, so the cleaning and height adjustment to one of the main pipes going out to the split didn’t work yet. Still banging at night. So irritating!! Thanks for all the help and suggestions.
Whats the pressuretrol set at maybe they didn't lower the setting ? On another note when i do a cleaning even on a new install the lwco probe gets removed and cleaned as does the pigtail dirty boiler tend to clog the pigtail plus aside from the factory pressure gauge a decent 0-3 psi gauge is a standard on my installs i don.t think that breaks the bank .I would also kick that cycle guard lwco to the curb and install a non cycling low water cut off . That cycle guard is insurance policy for mis piped boiler cause problems always appear when ya finally building pressure and a boiler which intermittently cycles off hides those issues but it can in some cases of lower water volume from original system work out but in general i just about always remove and upgrade to a non cycling lwco and leave the old cycle guard and its extra probe there . As in some cases of mis piped boiler that cycle guard works out and hides poor installs and single use of tapping especially on side outlet boilers
peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
I am in suburban Chicago, this installation would not have passed the building inspection. We have a high water table, busting up the floor and filling it with gravel is not acceptable, every decent rain my basement would flood with that hole.
If this homeowner had a 10% or more retainage or holdback until the system was proven to meet expected or promised performance, he would at least have had some extra cash to pay for its correction, just sayin. My guess is these installers have no clue how to resolve the problems they created based on above post. And, these installers likely went to a local bar after collecting the balance due drinking over what a loser the homeowner is for paying for an untested system. Is the homeowner getting charged for the installers returning to fix problem they created and unqualified to fix after paying 18K?
These scam unqualified steam boiler installer posts are all over this site again and again…..
Regards,
RTW
Also, it’s irritating to hear that Dunkirk is not a great boiler. I asked about them and also tried to do some research, but there is not that much info out there respectively.
It’s not horrible. I had one piped way worse than yours and got it working well without dramatic changes.
Is it possible that this is only a skimming issue and it can be resolved with enough cleanings?
yes it is possible. Have you had a chance to view the water level during the banging?
There can be a couple ways banging can occur but if you see the water level dive, that is verification that it is surging and should be solved by oil removal through skimming
Clammy has so much knowledge but one question I always have about insulated mains—how could there be too much condensate in the mains—they are already carrying ALL the condensate regardless of insulation. Just a small digression since he brought it up
CLAMMY's Post above is worth repeating in this matter:
"I will give them some credit they did it in steel pipe which in nj is not the most common thing seen on steam boilers being not everyone is the mind set of doing the completely right job only a few idiots out here . And i know i lose to these types all the time but that's fine by me ain't my house ain' t my bills ain t the one putting up w it . Sorry if it comes off arrogant or elitist but after you see this shadiness and bull all the time on alot of jobs it gets to ya and after a while you stop putting up a good argument as to your price and let them have some one do the job and then they realize they did not get what they though they where getting but got hosed and of course re do are always about as much money as the garbage install was . Just cant make it up living the dream!
peace and good luck clammy"
Regards,
RTW
My 45 year old boiler has water that is super clean and never bounces more than a quarter inch now due to extensive cleaning and the appropriate addition of Rectorseal 8-way.
What I can say is that before coming to this site and becoming an educated homeowner…my water would look nasty like yours after awhile. I would know it was time to flush/clean the boiler because I would start to hear banging. The water would foam, surge and disappear, only to return shortly after the boiler turned off.
This is your picture that I've zoomed in on. This is exactly what my boiler water would look like when it behaved exactly how yours is. It needs to be flushed out and fully skimmed multiple times. I can't even tell where the water level is in your site glass.
Paul the reason i always push for insulation is aside from being put on before we where born and it does serve a purpose is .
1 Improve even steam distribution even w perfect main venting a uninsulated steam main will never deliver steam to the run out or rads evenly being it has to heat the main and run to a point where it not turn back to condensate plus it still may be steam but at a lower temp being its losing temp till the main pretty pretty hot
2 pipe grooving and leaks yes a steam main will always have condensate forming and running to a wet return or dry return .The issue is when a steam main is un insulated there is much more condensate being formed on start up till that main is hot . Most leaks i encounter on steam mains are usually on uninsulated mains just about always . And w always comes at the joints the thinnest section of the piping it aint a coincident, i would think . Yeah ya get leaks on piping sags water seating and undervented steam mains but usually the water hammer gets you there first
3 Waste of fuel . Plain and simple and i know this as one of the four noble truths . In a distance past i work for a bit doing oil service and installs and advised more then a few customer's upon there complaints about fuel usage and over bearingly baking basement to insulate the steam mains and take offs . I quoted them a price and did the work all where completely amazed at the total difference the insulated piping made from the basement not being 100 degrees to radiators that would never heat now are working . They also had the benefit of using less fuel and being able to lower there stats and finally have even steam distribution . Everyone of them reported using between 20 to 30 % less fuel . That may not seem like much but if your burning 4 to 5 gph its something .
4 Banging not everyone basement is sealed some are like a open barn door in which case you can except some banging from time to time ,cold pipes heating up vacuum forming and bang and again waste of energy
aside from all that its the right thing to do if you want to do it right as the dead men would have done and yes everyone hates insulation its itchy so what grow up man up and either do it or pay a insulation company to do it .
Here's some thoughts if ya think bout it in nyc every heating/cooling pipe on new work has to be insulated its energy code ,even if its low temp radiant .
drips bangs and leaks just food for thought
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating2 -
Did the new boiler bang the first time it was used, or was it perfectly fine at first and slowly started getting noisy after a few hours, or days?
Thanks for your generous description there Clammy. We can definitely agree that insulating the mains keeps unwanted heat out of the basement and into the areas where it's desired.
It looks like there are 3 things happening here:
- The riser out of the boiler is too small:
This shouldn't be reduced with a bushing so the steam velocity is higher so it carries more water with it. The physics of the side outlet boiler also tend to carry more water with the steam vs a top outlet.
2. It needs to be skimmed through this tapping but with a reducer to raise the height of the water level that is flowing out of the skim tapping:
Without the reducer the level of the water will be below where the sections join and the oil willl stay in the inner sections of the boiler.
3. It looks like there is too much additive and the water is foaming, this foam will carry liquid water in to the mains:
This is also incorrect although probably not causing your issue:
It should do this:
The header should be extended and loop around to where the equalizer drops and the header should slope toward the equalizer.
1 - The riser out of the boiler is too small:
Nothing wrong with Dunkirk they have been making boilers for years. Many on here will say you should have done this or that. Dunkirks has been making side outlet tapping boiler and they work fine IF installed right.
They may not be the first choice of some installers but they are not JUNK.
Many rail about pin type boilers (usually oil boilers) and say three pass boilers should be installed and then they go out and install pin boiler themselves. Nothing wrong with pin boilers and the efficiency is fine. Pin boilers may be slightly harder to clean and maintain the flue passages.
Your problem is with the installer. I dislike having to criticize the install because the installer knew how to pipe. Most of this is nice and neat and straight. He just is not as well versed as he should be on STEAM piping.
Here is the fix. READ the dam manual. It's all in there. You and the installer both need to read the manual especially the piping diagram.
YOU shouldn't have to read it but you have to because you can't trust the installer. He should have piped the boiler with the correct size pipe (and in the correct configuration) according to the manual and skimmed the boiler.
It's as simple as that.
9 -
This is how jaded I am getting, I was just happy it had black pipe and a header with things in the correct order 😅
Hey @EBEBRATT-Ed and All, doesn’t this look correct? Pipe size, set-up, etc.
That's why i said check the manual. Usually it doesn't allow it to be reduced but it looks like that model allows it. I would look closely at the section on skimming to see if it requires the reducer that @The Steam Whisperer mentioned to get the water line above the sections but fails to show it here.
Seeing the manual it probably just needs flushing out of that additive that is foaming and skimming a couple times.
Hmm. Sorry to hear that. So if it was working ok, why'd you replace it?
Those Arcos may not be the most efficient, but the do last pretty much forever.
Now looking at the manual it doesn't look so bad if the boiler is a 3 or 4 section. But he should have planned things out a little better. Mostly I don't like the equalizer. It should drop straight down. If it can't drop straight down 45 degree elbows are ok above the water line but not all the 90 degree elbows. So basically what I am saying is that the equilizer should have been positioned where it could drop straight (or mostly straight down) and then change direction below the boiler water line and not above the boiler water line.
Where are you hearing the banging?
If it is around the boiler and the header the equalizer may be part of the problem.
How is the boiler water level when it is steaming?
Is it jumping around and moving more than 3/4-1" or is it steady? Any water in the sight glass coming down from the top of the sight glass…the top sight glass tapping.
If it is banging out in the system, it more likely needs skimming. I would use washing soda or TSP and boil the boiler out and skim it
- It wasn’t getting heat to the far end of our home easily.
- Mechanisms stared breaking (gears) and nobody wanted to touch it.
- It was costing $400-500/month in the winter
- Winter was coming lol
@EBEBRATT-Ed level is definitely jumping around by 2-3 inches
That water is clearly full of manufacturing oil, dirt and whatever. It does not look like it has been skimmed to me, at all. Ed is right, it needs washing soda/powder then skimming.
The equalizer doesn't bother me because I know once the water quality is good on this little boiler, there will be no water carrying into the header even with the undersized pipe.
You should see just how much I can throttle down my supply pipe and it's just fine. Steam can squeeze. I'll show you in a video soon. Edit: I made the video and here it is
@ethicalpaul don't forget he does not have the excellent piping and drop header you have he has 1 2" supply. The equalizer may come into play here.
I say skim it and try it. I wouldn't repipe the equalizer unless it doesn't work.
You need to look in the boiler manual and find out how much water you boiler hold at the normal water level. Then buy some Arm & hammer washing soda. 1 pound does 50 gallons of boiler water so you have to figure out how much to put in based on how much water your boiler holds.
Drain the boiler to the bottom of the sight glass.
They may have to take the safety valve off the boiler to add the soda.
Mix the washing soda in some water in a bucket and pour it in the boiler through the safety valve opening.
Replace the safety valve
Fill the boiler to 1/2 a glass
Start the boiler and run it until the supply pipe just starts to make steam and shut it off
Make sure the boiler has no pressure and take off the skim plug. Put a 2 1/2 x 1/2 bushing where the plug was
Put a bucket under the skim tapping
add water to the boiler slowly until it comes out the skim tapping
Adjust the water feed you only want the water stream to come out the size of a pencil
Do this until the water is clear. It may take an hour or so.
Then drain the boiler replace the skim plug, Or better yet install a 1/2" valve on the bushing.
When the boiler is cool enough fill it up to the top of the gauge glass…then drain it. Do this 2 times
Then refill the boiler and run it normally and see how it goes. This first time may get rid of all the oil but you may need to do it again but I doubt it.
3 -
Looks like Dunkirk changed their manuals…They used to be 2 1/2 inch minimum on all sizes for the header and riser. If that piping is up to the manufacturer standards, then I'd really go after the dirty water. Install a skim port and start skimming and flushing the boiler.
To learn more about this professional, click here to visit their ad in Find A Contractor.4 -
This:
Is not acceptable. Agree with the above:
Flush, clean with TSP or equivalent, flush again and skim until the water is clear AND there's no surface layer of oil.
I have 8 way in this boiler, hence the color, but notice it's clear.
Regarding the banging, I think your Hartford Loop is too high. The crossover needs to be below the waterline.
But clean up the water first, as that may be a solve in itself.
The water line is surely an issue. Skimming another.
@EdTheHeaterMan Is this a situation where a false water line can be installed to correct this issue? I've never done one before but it sounds like the cure to me.
Or is it an issue when the "new" boiler has a water line that is too high?
Compared to the old one? No.
Strange, when I went to Dunkirk's web site they were still showing 2-1/2" recommendation for the supply and also the header.
But anyway, as I indicated I might do, I made a video showing how steam is very flexible and squeezable and can still perform OK even when the installer isn't great and uses piping that is too small. Here it is.
If there are wet returns that are no longer wet returns then a False water line will fix that . I just can't tell for sure unless I look at the way the returns are configured. And there is no chance of that happening. did you look at the steam school video? the time stamp abut 2:24:07 is where the false water line is discussed.
I did not. Ill take a look. Thanks for the tip.