American Standard EP-68 electric boiler Aquastat
My American Standard EP-68 electric boiler water temperature is hovering at 200° while set for 160°. The thermostat is set at 62°, but it’s 68° in the house. I know I need to replace the t-stat as the heat does not shut down when the thermostat is off. My main concern is the water temperature in the boiler and I suspect it’s the aquastat. I can not find any repair company that knows anything about electric boiler furnaces to come out and look and I’m unable to find anywhere that has parts. Please help. If I can find an aquastat, I’m sure I can find an HVAC company to replace it. Aquastats are aquastats, are they not?
Comments
-
electric boiler furnace?
0 -
it heats my house, I call it a furnace. It’s a electric boiler for heat. What would you call it?
0 -
It's a boiler. Electric powered, but a boiler.
The aquastat is probably quite ordinary — first thing I'd want to check is what it is actually set to. It does have calibrations on the dials…
The thermostat not shutting the boiler off may — or may not — be the thermostat. Before you fire the parts cannon at it, try simply disconnecting it. If the boiler turns off, OK, probably the thermostat. Also try setting the control to some lower temperature? It turns off? Out of calibration. If it doesn't turn off if disconnected — it's not the thermostat and you need to look further. Disconnect the thermostat wires at the boiler end. Does the boiler turn off now? Wiring problem. And so on.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I’ll shut the power off, disconnect a t-stat wire and take it from there.
Still need a parts source. Any recommendations? If only for future reference
0 -
Part's source? Depends so much on what is needed. Sometimes Amazon, believe it or not, or one of the big box home stores. Sometimes a good hardware store. Sometimes a specialty supply house.
Trouble is, with any of those, you really need to know quite precisely what you are looking for.
Try us — we try to be helpful.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Shut off power to boiler. Disconnected one T-stat wire. Powered boiler back on. Heat came on. Now what?
0 -
That sounds, unhappily, like a wiring problem. Next test is to go to the boiler and find out where those thermostat wires connect and disconnect one of them there. If the boiler behaves now… probably is the wire from the boiler to the thermostat.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I did disconnect the thermostat wire at the boiler. Turned the power back on to the boiler and heat is coming from the radiators.
0 -
OMG - I feel like an idiot! It was only 2 blown fuses!!
0 -
if you're fixed, you're fixed, but,
can we see pictures?
not sure how blown fuses makes heat stay on,
can you show fuses you replaced, wide angle,
known to beat dead horses0 -
Sometimes fuses blow for a reason.
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements