TACO Outdoor Air-Sensor: Wiring Help Needed
Trying to understand wiring on the PC700-2 Boiler Reset Control. But only for the Outdoor Air-Sensor (Taco 9300-2052). The outdoor Air-Senor has only two wires - red and white. Red wire was traced to the "Out" on the PC700-2 Boiler Reset Control. White wire is traced back to the "Common" on the PC700-2 Boiler Reset Control.
The outdoor air-sensor has two screw terminals. Both terminals are labeled the same ""S1".
How do I determine which colored wires goes to which terminal on the outdoor sensor?
Please see attached picture of the Outdoor Air-Sensor and the two terminals I am referring to.
Thanks in advance for any assistance.
Comments
-
It shouldn't matter. I think it's just a thermistor.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you for the reply. I thought that as well. But when I wired it up. It shows the "OPn" Trouble Code.
See pics.
So I assume something is wrong.
0 -
connect the sensor right at the control. That will eliminate bad wiring
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Cycle the power to the controller so that it will do a reboot and look for the sensors.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements