TACO Outdoor Air-Sensor: Wiring Help Needed

TheSpad
TheSpad Member Posts: 3

Trying to understand wiring on the PC700-2 Boiler Reset Control. But only for the Outdoor Air-Sensor (Taco 9300-2052). The outdoor Air-Senor has only two wires - red and white. Red wire was traced to the "Out" on the PC700-2 Boiler Reset Control. White wire is traced back to the "Common" on the PC700-2 Boiler Reset Control.

The outdoor air-sensor has two screw terminals.  Both terminals are labeled the same ""S1".

How do I determine which colored wires goes to which terminal on the outdoor sensor? 

Please see attached picture of the Outdoor Air-Sensor and the two terminals I am referring to.
Thanks in advance for any assistance.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,556

    It shouldn't matter. I think it's just a thermistor.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • TheSpad
    TheSpad Member Posts: 3

    Thank you for the reply. I thought that as well. But when I wired it up. It shows the "OPn" Trouble Code.

    See pics.

    So I assume something is wrong.

  • hot_rod
    hot_rod Member Posts: 23,108

    connect the sensor right at the control. That will eliminate bad wiring

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Dave H_2
    Dave H_2 Member Posts: 579

    Cycle the power to the controller so that it will do a reboot and look for the sensors.

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions