Cast Iron Steam Radiator maximum pressure.
ssnowder
ssnowder Member Posts: 7
I work at a prison built in 1939. The steam supply pressure to the housing units in 85 psi. This is, of course, reduced at the housing unit mechanical rooms. However, there are a couple of offices that are operating their radiators at 80 psi. Until I can find some reference to the max allowed psi, they refuse to stop using them. So, can someone provide some manufacture or other source for max allowable pressure? Thanks!
    mattmia2 Member Posts: 16,426
    you would have to figure out who made them and find a catalog for a definitive answer but 10 psi steam and 30 psi hot water would be a good absolute limit absent any other information. unless you are doing some condensate lifting with steam you only need a couple ounces of pressure to fill the system with steam. 80 psi steam contains so much energy and volume of team that it will suffocate and scald you if a pipe breaks.
    ssnowder
    yeah, there is also the problem that what would be hammer at 5 psi is an explosion at 80 psi so you have to be extremely careful that the system is maintained properly and even things like opening or closing a valve can be deadly.
    ssnowder
  • CLamb
    CLamb Member Posts: 348
    Old time railroads referred to it as the "white death".