RAY 200I BOILER FLAME FAILURE
thelabman1
thelabman1 Member Posts: 2
I have a RAY 200i boiler, I live at 7,000 feet.
When the outside temperature stays below freezing the boiler will go in to alarm for flame failure and shut down.
I have replaced the flame detector rod and the control board for it.
It runs great during the spring, summer and fall, but when I drop below freezing for winter it goes into flame failure.
    Jamie Hall Member Posts: 27,355
    What is your fuel? LP? Oil? It sounds remarkably as though something is freezing up — for LP, it might be the regulator (there is supposed to be some methanol in the LP to absorb water, but… there might not be); if it's oil and the tank is outside or where it can get cold, it might just be that the oil is gelling. There is an additive for diesel which stops that, but it might not be in the heating oil you are getting.
    So… what is the fuel? Tanks inside or outside?
    109A_5 Member Posts: 3,978
    If this is the boiler: https://wizard.youngsupply.com/files/182-o110101.pdf Mestek rAy Cast iron condensing boiler 200i it can run on LP or Natural Gas.
    I agree with Jamie, sounds like a freezing situation, maybe water in the fuel line at a low point where it could freeze. Once in flame failure was the fuel availability verified ?
    HVACNUT Member Posts: 7,434
    edited November 2024
    Vent or intake freezing?
    Condensate draining?
  • thelabman1
    it is natural gas
    no water in the line
    EBEBRATT-Ed Member Posts: 20,164
    edited February 2025
    I would check the gas pressure at the boiler inlet when it (the boiler) is ok and when it is not. Maybe have the gas utility out to check the meter.
    If you have any gas regulators in the system check the vents for bugs, wasp nests or water/moisture. The water or moisture could freeze when it gets cold blocking the vent and the reg will not work.