No Air Elimination on a 2 pipe
Yesterday I went to a steam boiler that was piped in two pipe with a condensate receiver. The plates had separated after only 12 years and a myriad of other people were there before me and essentially ruined this boiler. I wont belabor the amount of nonsense I saw but I could not find a single Air vent on the entire system. Could the air vent pipe on the condensate receiver be the only needed air elimination in this system?
Pictures included
for fun! My favorite part is they put a tee and pump off the condensate return pipe to pump the condensate through a copper fin baseboard in a remodel a plumber did for them 12 years ago when they also installed a 1,040,000 btu steam boiler that only needed 500k btu at MOST due to the massive amount of radiators removed and modern furnaces taking the heat load in those areas of the home.
No vents or crossover traps? Weird.
But I'm not a 2 pipe guru.
Yes, that tank vent can serve as the vent for the entire system.
But- you say this is a home? Why is that tank even there? From the pics it looks like there should be enough height for the water to return by gravity.
The boiler looks like a Weil-McLain LGB. These boilers will leak if not properly piped. Did you take a pic from the front of the boiler?
Consulting2 -
My steam system (residential) is two-pipe with a condensate receiver and the only vent is on the receiver. There is limited height and the system with this boiler probably requires a pumped return. For the most part it vents fine, but it has a water sealed return that does not vent that I have posted about.
I don't think it is or has ever been a vapour system, but I don't know how to tell for sure.
YES. Ventless systems existed but once alternate air elimination no longer…..
- 117 Geothermal
