Weil McLain steam boiler and water treatment
I have a very slugged up Weil McLain steam boiler in a duplex unit that I am currently in the process of cleaning out. I typically use 8way water treatment in all my steam boilers to keep corrosion down but I know you have to be careful with what you put in Weil McLain’s due to their gasket materials. (No petroleum products) I talked to rictorseal and they were not a huge help but did say 8way would be fine, then I talked to Weil McLain and they did not have any recommendations for steam water treatment. Just wondering if anyone has ever used a water treatment in McLain steam boilers or that’s a no fly zone.
Thanks
Comments
-
I should probably add that out water is pretty good here and the source of the sludge was excessive make up water due to a steam leak. Leak is now fixed but sludge is giving me a run for my money…..good thing the basement is not finished…..HA!
0 -
It might take some time to get all the sludge out, but 8-way will help, just don't overdo it. Add a little, let it free up some gunk, drain a little mud out the bottom, repeat. Eventually you want to get to where you don't have to drain very much.
It has basically the same ingredients as the old Steammaster tablets had. I never have heard anyone have any problem in a Weil-McClain with typical boiler treatments.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
I’ve never added any type of water treatment to my steam boiler. Is this something I should do ? I have the same system. I never see much build up in my sight glass. I cleaned the system and flush it on my own yearly.
0 -
In my strong opinion, anyone with a recent vintage boiler would be a fool not to keep the PH at 10-11 and minimize draining. In the olde days, the castings were insanely thick apparently, and a boiler could last 100 years with just regular water (see Cedric).
That's not the case today.
But I believe that with just minimal treatment and attention to the water, you too can have your boiler outlive you. In your case I would strongly consider not draining the entire boiler. Just drain enough until the water runs clear. Then add just a little 8-way (my favorite additive)— like 3 ounces. It will free up some gunk. Let it run for a couple weeks. If it surges (marked by a dramatic drop in the gauge glass during steaming), then drain and refill and again add a little 8-way. When the water is finally staying clean, it will hardly get dirty at all if you keep the PH at 11.
When you drain it yearly now, does the water start out brown and then go clear after a gallon or so?
Shameless plug for my video showing my year-long corrosion experiment
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Quoting Ethical Paul
}In my strong opinion, anyone with a recent vintage boiler would be a fool not to keep the PH at 10-11 and minimize draining."
If we only had to consider the effect of pH on cast iron and steel, I would totally agree with you. However,
Weil-Mclain strongly suggests that pH in a steam boiler be maintained in the ranger of 7 to 8.5. They firmly state that a pH of 9 is high enough to damage the elastomeric seals that they use between the cast iron sections. Yes, ask me how I know. Ha! My WM680, installed in Dec. 2012 started to leak. It was only apparent on a cold startup when I restarted the boiler during a late season cold snap at the end of the 2024 season. I got excellent response from the installing contractor, the distributor, and a very knowledgeable representative from the Chicago office of WM. He took a sample of my very clean Steammaster treated boiler water back to the lab. It tested at 9 pH. They stated that was the cause of the seal failure. In checking the current edition of the installation manual, they DO call out the pH limits for the boiler.
In my case, we did a teardown and seal replacement. We caught it early enough that there was no damage to the cast sections. Boiler is running fine now. I will monitor pH and chloride level going forward. It's a very tight 2000 EDR 2-pipe Dunham system running under induced vacuum part of the time. Only added 18 gallons last year.
Again, WM limits pH to a max of 8.5
Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com3 -
Wow, that is kind of alarming. If 8.5 is fine and 9.0 causes the destruction of their seals, that is a problem. Even though the PH scale is logarithmic, it's very difficult to try to hold a line between 8 and 9 PH. I have seen in the WM manual they do say 7-8.5
If your story is true, and I have no reason to disbelieve you, I would not recommend a WM boiler.Did they deny your warranty claim based on 9 PH in your boiler?
Only added 18 gallons last year.
Only?? 18 gallons is kind of an outrageously high amount of water to use in a year!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Hmm… contrary to firmly held belief, any pH more basic than about 7.2 will protect iron just fine. Many people seem to like to drive the pH way high, but it isn't needed to do so for corrosion protection.
Cedric is a Weil-McClain, and is doing just fine with pure well water — for many years now.
And yes, 18 gallons of water is out of line. Find the leak(s).
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
a lot of steam manufacturers and professionals would disagree that 7.2 is good enough to inhibit corrosion.
Of course a lot of manufacturers and professionals erroneously think the equalizer affects the “A” dimension so I’m hardly one to rely on an appeal to authority argument.
Do you have any data to back that 7.2 value up? Not challenging, but honestly asking.
I don’t put a lot of weight behind Cedric—he was built when castings were far different than they are today I believe. He probably could have survived this long with vinegar in his veins. Out of curiosity, does Cedric have the elastomer gaskets that modern W-M boilers have between sections?
Info that I find says that in the range of 4 to 10, normal corrosion occurs, and a somewhat protective layer of normal iron oxide forms. I think we see this inside our old main pipes and return pipes. Below 4 the acid removes the protective layer leaving the iron exposed to faster corrosion. We see this when people use vinegar or other acids to remove rust.
But at 10+, a different oxide is formed that causes corrosion to dramatically reduce (I am not a chemist):
Some DOE nuclear power article about iron corrosion
This article also notes that de-aerated water at high temperatures (with chart shown at 580F), corrosion starts to swing back up above 12.5 PH. I don't know if this affects de-aerated water at 212F but this chart fits with the non-Weil-McLain manufacturers' recommended high-end of 11 PH.
Other articles I found generally put it like this (my emphasis):
Within the acid range (pH <4), the iron oxide film is continually dissolved. In cooling water, the potential for calcium carbonate precipitation increases with higher pH and alkalinity; thus the corrosion rate decreases slightly as pH is increased from 4 to 10. Above pH 10, iron becomes increasingly passive.
Edit: I think I found the article that is the source for a lot of these other references on the internet. It is related to corrosion via pitting in nuclear containment vessels.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el-1 -
Yikes. Our Weil McLain steamer has a ph of about 10.5 thanks to 8 way. I’m thinking of draining/adding some water to drop the ph a bit.
0 -
Cedric is a plain vanilla Weil-McClain 5-80. Yes, it does have the elasomeric gaskets (which will last forever, unless they are installed incorrectly or subject to base attack).
And you are quite correct, so far as I know, about the iron oxide which forms with the pH between about 4 and about 10. Perhaps more to the point, it forms at 7 to 8.5 perfectly happily, which is why I suspect that WM doesn't push higher pH values. It's the same oxide that the pH 10 range folks are pushing, so I myself don't see the point. You're not hanging anything…
On the other hand, so long as you are able to adequately buffer the water so it stays in the 9 to 10 range, you aren't hurting anything, either.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Respectfully, the articles I have been reading do in fact say there is a different oxide that is forming at greater than 10 pH. Refer to my links above or search on your own. It seems to be a difference between iron oxide and iron dioxide.
I admit I'm a little disappointed, I had pictured Cedric like this all this time:
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el3 -
No, sorry @ethicalpaul !
And you are quite correct in the difference between various oxides of iron. There are two fundamental differences: Ferrous (Iron plus 2 valence) and Ferric (Iron plus 3 valence), and oxide (0xygen minus valence) and hydroxide (Oxygen/hydrogen covalent bond, minus 1 valence). They can be mixed, either physically or in a chemical mixture. The solubility of the various possible combinations (there are at least 12) varies with pH, but they are all soluble to at least some degree in acid (pH less than 4) water. None of them are particularly soluble in neutral to basic (pH greater than 7). Upon reacting with oxygen, the oxide forms — and it expands. Some of the oxides, however, form relatively good bonds with the underlying iron (or steel) while others tend to flake off. Fortunately, most of them do form decent bonds.
Of note and real importance is that once Iron is oxidized, either to ferrous or ferric iron, the presence of carbonic acid, sulphuric acid, or chlorides yields soluble free iron ions, and the rust instead of more or less staying put simply washes away. The presence of the two acids is minimized or eliminated by keeping the pH neutral or above provided the water has at least a minimal amount of Calcium (both the Cabonic acid radical and the Sulphate radical combine with the Calcium to form an insoluble material at neutral and above pH) with the presence of chlorides can be reduced only by ensuring that they are NOT present in the water (note that this is why the use of salt softened water is so lethal to boilers).
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Thanks for that! I will add that in some of the articles I read, they said that with pH above 10, the calcium carbonate precipitates out and that's why they see corrosion drop way off at that pH, because the passivity of the nice solid oxide layer remains in its protective position!
It's a shame that WM boilers can't experience that, at risk of their gaskets!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I've never treated or tested the boiler water since I bought the place 4 years ago. When I drained the water, just before turning it on for this season, it turned clear after about 4 or 5oz. (maybe less). The water in the sight glass is clear. I'm assuming i don't need to touch it.
It kills me that the previous owner drained and refilled the thing monthly. Can't imagine how many years of life he took from it.
Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators heating up 3800sqf.1 -
Well if it never produced any more mud than what you're seeing, he might not have taken any years of life from it. If it's turning clear after 4 ounces of draining, I'd say you are good.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
I hope so. Thanks
Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators heating up 3800sqf.0 -
My ph via a meter was 10.6 with 8 way. I drained the water down to within an inch of the bottom of the sight glass and refilled. The ph was still around 10.5. I then repeated the process. I haven’t rechecked ph again. I know in WM manual it does say to keep ph max 8.5. Should I keep at this? I’m just concerned about the prongs between the sections.
0 -
8 Way is a very good buffer. Unfortunately the stable range is pH 10 to pH 10.5, which is fine if that is where you want it.
However. Since it is a very good buffer, you will need to get almost all of it out of there to get the pH to move much out of that range.
Up to you. Some here say that the boiler should be kept in that range, and the manufacturers are clueless. Some here say that anything more basic than 7 is fine. Some say you should follow the manufacturer's opinions.
Some of us just run tap water and have for years with not problem at all…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Up to you. Some here say that the boiler should be kept in that range, and the manufacturers are clueless.
I'm not sure I've ever heard anyone here say the manufacturer's are clueless (certainly I haven't). Several manufacturers (including mine, Peerless) recommend a high end of 11. I know you don't want to put words in anyone's mouth 🙂
Unfortunately the stable range is pH 10 to pH 10.5
Or fortunately
@Don_175 take another measurement and see where it is now.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Probably shouldn't have said "unfortunately". However, the point is this: the buffer range of the 8 way seems to be from 10 to 10.5. What that means, however, is that the concentration of 8 way — the amount present in the water or initially put in — can vary over an extremely wide range, but the pH will stay in that narrow range. This is why buffers are so handy! But also why they are pesky — once there is any significant concentration of a buffer system in the water, that's the pH range you are going to have. If it's what you want, you are delighted. If it's not what you want, you are left with no choice but to get rid of the buffer system and start over…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
The ph buffers are pretty strange when one is used to thinking about traditional mixing of stuff to get a result! I was reading about chemistry students who set up different solutions then they mistakenly contaminate something with a buffer, and the whole thing is shot!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I completely emptied the boiler and refilled it with fresh water. The ph is now about 9.7.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements