Is there an ideal cycling time for oil boiler run time cycle? What is short cycle?

What is a typical on/off run cycle for a well tuned steam system? Say it's 30F outside, and the thermostat is set for 67F. Should the boiler run for X minutes, and be off for Y minutes? Ballpark ranges? How does one dial this in? Vents?

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,157

    A good steam boiler cycle rate is one cycle per hour. That is what the thermostat sees.

    What the burner sees may be quite different. During a call for heat, if your boiler is oversized, the burner may run for 10 minutes to make steam and pruge the air out of the vents. but if the thermostat is not satisfied by then, then the steam pressure increases and may trip the limit on the pressure control, 4 minutes later the pressure will drop and the burner will come back on. The pressure will build for some short time and pressure control will trip off again is a minute of two. And this cycle will go on until the call for heat is satisfied. So you need a proper size boiler to get your best oil burner or gas burner efficiency.

    If you have got it just right, then the pressure limit control will never trip and the burner will stay on for 40 minutes and shut off for 20 minutes at 30°F

    At 40°F the burner may run for 30 on 30 off.

    AT 10°F the burner may run for 50 on 10 off.

    Hope this helps

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MikeAmann
  • LRCCBJ
    LRCCBJ Member Posts: 291

     During a call for heat, if your boiler is oversized, the burner may run for 10 minutes to make steam and pruge the air out of the vents. but if the thermostat is not satisfied by then, then the steam pressure increases and may trip the limit on the pressure control, 4 minutes later the pressure will drop and the burner will come back on. The pressure will build for some short time and pressure control will trip off again is a minute of two. And this cycle will go on until the call for heat is satisfied.

    ^^^^ THIS is short cycling.

  • skimmer
    skimmer Member Posts: 52

    Isnt this what all steam boilers do? In a perfect world wouldnt it never build pressure before satisifying the tstat?

  • LRCCBJ
    LRCCBJ Member Posts: 291

    Let's say that MOST steam boilers do this…………simply because nobody bothered to measure the radiation before specifying the size of the boiler………..and the perpetual tendency to "go larger because you don't want to be caught short on a really cold day".

    Additionally, the issue develops when the near boiler piping is not done well and the steam is carrying more water than desired to the radiation………….which is less capable of dissipating it.

    It is, however, eminently possible to install a properly sized boiler with a drop header that develops very dry steam and NEVER develops pressure above several ounces during continuous operation. Every lb. of steam developed is dissipated by the radiation.

    My personal opinion is that the radiation does not have a fixed output. The output is somewhat variable depending on the water content of the steam. The less water, the greater the output.

  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    Not all steam boilers by any stretch. A properly sized one will in theory never cycle, as @LRCCBJ . However on very long runs even most very accurately sized ones will eventually hit a pressure limit on the order of a half pound or so, at which point it will shut off and let the system catch up and then restart, perhaps very quickly, and run again for a fairly long time (assuming the thermostat doesn't turn it off).

    Further, as @LRCCBJ said, the ability of the system is somewhat variable. Water content is one part, but at least as big a part is the temperature of the space and rooms which the radiation is powering. A cold space will absorb more heat from a radiator than a warm one, and the difference is significant.

    So some long term cycling is to be expected.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • skimmer
    skimmer Member Posts: 52

    So i raise the temperature by 4 degrees let’s say from 68 to 72 once the steam starts coming up my boiler should continuously run until the thermostat is satisfied? Never shutting off on pressure ?

  • ethicalpaul
    ethicalpaul Member Posts: 6,433
    edited October 28

    Ideally yes but this can be hard for even a correctly-sized boiler to achieve (not least of all because the standard pipe-loss factor is too large).

    Isn't this the same question you asked before and that @Jamie Hall answered?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • skimmer
    skimmer Member Posts: 52

    I don’t remember if asked this before. Maybe a few years ago??

  • skimmer
    skimmer Member Posts: 52

    Oh ok I didn’t see it that way. I don’t think I’ve ever had my boiler run continuously (burnham in4) without cycling on pressure before my tstat was satisfied. And I believe my system is in good shape. Properly vented , balanced, etc. i have copper fin tubing radiators instead of cast so I don’t know if that has something to do with it.

    No hissing vents. All rads heat at the same time. Small house. Boiler doesn’t shut of on pressure before i get heat. But I’ve never had it run continuously on low pressure until my stat was satisfied ever.

    I would like to but I just can’t get. even have a main vent at the end of my one main which is about 30 feet. And I even have dual drop headers!

  • ChrisJ
    ChrisJ Member Posts: 16,234
    edited October 29

    I just want to add.

    Honeywells cycles per hour, is roughly how long it should run at something like 50% load.

    Meaning, at 50% load it'll run 30 minutes on 30 off. It can, and will run more cycles in an hour if the system is loaded heavily. It's just a rough way to describe a digital anticipator.

    How long the boiler should run is kind of irrelevant. It should run long enough, and be off long enough to keep your house comfortable under whatever conditions there are at the time. What mine does is completely irrelevant to what yours should do.

    Its shouldn't overheat the house.

    It shouldn't bounce off the high limit 5 times to heat the house for 10 minutes.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ethicalpaul
    ethicalpaul Member Posts: 6,433

    Oh ok I didn’t see it that way. I don’t think I’ve ever had my boiler run continuously (burnham in4) without cycling on pressure before my tstat was satisfied. And I believe my system is in good shape. Properly vented , balanced, etc. i have copper fin tubing radiators instead of cast so I don’t know if that has something to do with it.

    All that can be true and correct and still a boiler can cycle on pressure. It just means that the boiler is producing more steam than the attached radiation can condense, so steam pressure builds. Dual drop headers are unrelated to this issue.

    Have you ever measured the EDR of your radiators and compared it to the "Net Sq Ft of steam" rating that should be on your boiler?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    ChrisJ
  • skimmer
    skimmer Member Posts: 52

    I did a very long time ago. And came up with a number and in4 was the right fit

  • LRCCBJ
    LRCCBJ Member Posts: 291

    I find it impossible for the boiler to be the "right fit". Their ratings all have a 33% pickup factor, and, if you match that number to your radiation, you'll be 33% oversized (slightly less due to the piping losses). This boiler will always cycle on pressure…………..no way around that.

    There are folks that have installed a boiler with a 10% pickup factor and they work just fine. They take slightly longer to heat the entire system but they NEVER cycle on pressure.

    There are systems that might not behave well with 10% if they have extensive, uninsulated piping, especially if the piping is in unconditioned space, but this is the minority of installations.

    ChrisJ
  • Jamie Hall
    Jamie Hall Member Posts: 24,558

    I'm going to put this in two current threads on short cycling.

    And be blunt. It is impossible to design and build a system with a fixed firing rate at the boiler and a fixed load area which will reach full capacity of the load under all conditions, but no more (and thus, if modulated by cycling, never cycle).

    You can get close. Sometimes very close.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    SuperTech
  • LRCCBJ
    LRCCBJ Member Posts: 291

    The fact that at least five members of this forum have achieved exactly that………………notwithstanding. Maybe they all just got lucky.😉

    ChrisJ
  • skimmer
    skimmer Member Posts: 52

    well yes. By perfect fit I meant Not oversized. The in4 was the right call for the radiators and the pick up factor. Works well for its size. And compared to others with the same exact house (same builders) who have bigger higher input boilers (150k and maybe 175k) and who I imagine have higher steam output i did ok. The only problem was the first in4 lasted 15 years after developing a hole above the water line. That was a disappointment since my neighbors boilers are still running and I know they are oversized compared to mine. Oh well that’s life

  • ChrisJ
    ChrisJ Member Posts: 16,234

    Mine doesn't even cycle on pressure doing a 9f recovery. Does it produce enough to fill the radiators when the house is 20f? No idea that's not normal operation conditions but it'll sure being the temperature back up and then go back to normal worse case.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment