NYC Boiler Room - Smoke Alarm that will cut off boiler
Perfecto1
Member Posts: 1
Had to do a whole new Boiler room filing for a property in NYC and 1 of the requirements is to have the carbon / smoke alarm tied into the boiler so that it cuts the power to the boiler if the alarm is triggered. I cant seem to find the proper equipment needed.
https://www.kidde.com/home-safety/en/us/products/fire-safety/safety-accessories/auxiliary-devices/sm120x/
I found this accessory, but it seems it only send a signal to an external device and not necessarily kill the power .
Thanks!
Thanks!
1
I don't know specifically but if the alarm triggered you would have to use a relay with normally closed contacts to shut down the boiler.
You would have to find out from the voltage supplied from the carbon/smoke detector from the device mfg. to select a relay.0 -
This unit has a relay which closes upon alert.
I’d use this output to control the primary coil of the relay which controls power to the boiler.0 -
when I was tuning my brother's furnace, we had a smoke event. The nest co/smoke detector in the basement communicated with his nest thermostat and shut the furnace off. Probably not acceptable in a commercial environment but pretty cool for residential.
If you're in NYC, call Pronto Gas Heating Supplies (3 locations) and ask Tito if he's got any CO/smoke alarms with the interlock relay in stock. He probably does. That's where I buy mine from time to time.
Or if you've already bought a Kidde CO alarm, just purchase and add this:
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Kidde-CO120X-User-Guide.pdf
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2
- 15.8K Strictly Steam