Buderas motorized exhaust question
slateroof
slateroof Member Posts: 21
My house came with a 20 year-old Buderas natural gas boiler ( with baseboards). Last winter is worked ok. Had it cleaned this summer, but now there is a faint gassy smell in the basement. The smoke/carbon monoxide sensor has not gone off. Going to he back of the boiler, looking up at the motorized exhaust damper, it seems to open just a little ( see photos: first image is in the closed position, second image shows the damper at maximum opening, when pushed with a probe). Should it be opening more than this? Thanks for any comments about this!
  • Ironman
    Ironman Member Posts: 7,903
    edited October 2024
    It should fully open.
    DON’T operate the boiler unless it opens fully!
    You and your family are at a risk of carbon monoxide poisoning!
    You should have it checked immediately by a competent technician or the gas company.
    Bob Boan
    slateroof
  • slateroof
    Thanks for the warning. Any idea what could cause the damper to not open fully? Any way to manually open it until the technician arrives?
  • Ironman
    It shouldn’t allow the burner to fire if it’s not fully opened, so something is seriously amiss.
    No, I don’t see any way that you can safely bypass it under those circumstances.
    Bob Boan
    slateroof
  • slateroof
    postscript for this post: The technician removed the motor housing to expose the exhaust damper. It was not opening fully due to a sticky hinge. The damper is opened by the suction of the squirrel-cage fan, so any slight friction will prevent it from operating properly. Graphite would seem the proper lubricant for this high-temperature application.