Buderas motorized exhaust question

My house came with a 20 year-old Buderas natural gas boiler ( with baseboards). Last winter is worked ok. Had it cleaned this summer, but now there is a faint gassy smell in the basement. The smoke/carbon monoxide sensor has not gone off. Going to he back of the boiler, looking up at the motorized exhaust damper, it seems to open just a little ( see photos: first image is in the closed position, second image shows the damper at maximum opening, when pushed with a probe). Should it be opening more than this? Thanks for any comments about this!
Comments
-
It should fully open.
DON’T operate the boiler unless it opens fully!
You and your family are at a risk of carbon monoxide poisoning!
You should have it checked immediately by a competent technician or the gas company.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Thanks for the warning. Any idea what could cause the damper to not open fully? Any way to manually open it until the technician arrives?
0 -
-
postscript for this post: The technician removed the motor housing to expose the exhaust damper. It was not opening fully due to a sticky hinge. The damper is opened by the suction of the squirrel-cage fan, so any slight friction will prevent it from operating properly. Graphite would seem the proper lubricant for this high-temperature application.
1
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 987 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements