Identify/Source a replacement solenoid coil (White-Rodgers Intelli-Vent)
itgogitrev
itgogitrev Member Posts: 1
I am looking to replace a solenoid on my HWH that overheats and prematurely closes the gas supply to the burner mid-cycle. The coil doesn't have any P/N or SKU codes on it, which makes it difficult to identify. It is for a Rheem HWH with the W-R Intelli-Vent controller, model AP13845A (37E73A-316). I've attached a few images of the coil.
Hoping someone knows if there's a part that will work for it; hate to have to blow $200-300 on a controller over a $10 part.
———————— troubleshooting details below ————————
The current coil "works", but only for about 8-9 minutes when it first calls for heat. After that, the flame will go out on the burner and will not reignite on the programmed reattempts. I have to manually turn off the HWH and wait 5 minutes to restart it when it'll ignite again, but drop out after 8-9 minutes.
    EdTheHeaterMan Member Posts: 12,206
    That is a gas valve.  there are no serviceable parts inside of a gas valve.  Since you have opened it up, you have voided any safety feature that is built into that safety device, and any protection against failure of a catastrophic  nature (liker a Gas Explosion). Your insurance company may deny a claim that is related to such an occurrence.  Be safe… replace the entire part!
    Jamie Hall Member Posts: 27,380
    Before you get too far — are you quite sure it is the coil overheating, and not getting overheated for some other reason? Check the voltage and current draw.
    mattmia2 Member Posts: 16,825
    Did you check gas pressure and combustion air, especially through the screen to isolate the combustion chamber from any explosive vapors outside the appliance?