Leaning towards heat pump
Now the heat loss from the first floor into the older basement is only driven by the 12 degree difference, and isn't all that much. The heat loss into the slightly newer basement is driven by a 22 degree, more or less, difference. Since the floor constructions are very similar, the heat loss into the newer basement is twice as great, per square foot, as into the older basement.
If you fail to consider the entire structure as a system, I can see how one might be misled. However, if you do it should be immediately obvious that the warmer basement will mean less heat required to heat the first floor — and that therefore the heat "loss" which is keeping that basement warmer is not a loss at all, but is simply heat being used in a different place. Usefully.
The fallacy (partial) in your argument is the fact that the heatloss to the basement with the 12 or 22 degree difference when the boiler is present in the basement is not compared to the heatloss that would otherwise occur if there was no boiler in the basement.
Furthermore, you imply that all the standby and operating losses of the boiler are directly offset by the increase in temperature of the basement.
Again, you carefully and deliberately avoid the extremely large losses from the boiler that the basement itself disposes of very easily via the walls and thereby fails to warm the basement by any significant amount in most cases. Of course, Cedric (and other huge boilers) might be an exception if the basement is tiny (and the boiler is huge) but this is not the norm in most cases.
If you consider the entire structure as a system the ignorance of the losses via the basement walls and floor must also be considered or you will be misled.
Ah. Well, I stand corrected by superior knowledge and understanding of thermodynamics. Thank you.
I thought about this.
The problem is if I take my boiler, and the associated piping out of the basement, now I have frozen pipes.
So keeping at general area at least at a reasonable temperature, say 45-50F is a requirement. A necessary evil.
"Can't see the forest but for the trees."
Ya'll are running around in circles. Ask yourself, do you want your basement warm or cold?
If you want it warm insulate it well and make it part of the house, because the r-value of your typical uninsulated foundation is abysmal. And you are seriously losing more heat there than your attic if you have even a couple inches of insulation up there. Everyone concentrates on the attic but as Jamie pointed out radiation goes in all directions equally. Only the stack effect and the temperature gradient it creates causes more heat to be lost upstairs and good air sealing with even a little bit of insulation is enough to tip the scales back down to the basement.
If you don't want a warm basement, insulate the basement ceiling and completely exclude it from the house but then any heat from the mechanicals will be essentially lost. Even a small amount of insulation in the basement ceiling will ensure almost all of that heat from mechanicals goes into the ground or space and never makes it to the house. You will decrease energy consumption of the structure overall because of a smaller surface area exposed but will paradoxically reduce the efficiency of the heating equipment. Also have fun air sealing around every penetration for every wire, pipe and the basement door.
If you have any kind of mechanicals in the basement insulating it is the only sane option.
If there is nothing in the basement and it has no value to you as storage than excluding it is the sane option.
All these other arguments about the equipment helping to heat the house are missing point.
What's the R value of dirt?
And what temperature is that dirt, generally speaking?
I only have 2 feet of exposed foundation the rest is below dirt.
For that matter, what's the R value of 18" thick field stone? I'm guessing not great, but it's also not zero. And how does it compare to dual pane glass windows? I've never seen mine sweat…
You could always wrap the pipes in heat tape and insulate them. Or just move them up into the joist bays closer to the subfloor and insulate the joist bay. The energy use to keep those pipes unfrozen would be minimal compared to the energy used to heat an entire uninsulated basement.
The temperature of the dirt is a gradient going from about the same as the air temp and getting warmer the further down you go. Eventually its about 50f but where that is true depends on how cold of a climate you live in. Its why my freshwater pipes are 5ft in the ground here in northern Ohio but in Texas might only be 6". Which I think is insane no matter how warm it is, just ask residents of Houston about a couple winters ago. But...
But assuming a 50f concrete floor and a temperature of somewhere between air temp and 50 for the foundation means you are losing heat year around to the massive heat sink that is earth.
Edit: which means in the summer that cool earth helps you a bit, but in the winter it hurts you. I'm experiencing this right now. I've insulated my basement so well that my server cabinet, freezer, fridge, and dehumidifier(although it doesnt run much anymore! :) ) have heated my basement to a little under 80 even with the upstairs around 72. I'm trying to figure out how to cool it now in the summer. Lol
The reason there's a gradient is because dirt does have an R value.
So does snow for that matter.It's my personal opinion a house should have a basement, and that basement should at least be partially heated. 50-60F is fine, and it sounds like that realistically results in fairly low heat loss.
Perhaps that's why my dad's basement that just has a 94% direct vent furnace and duct board in it stays around 50-55.
But like I said, I never saw any of the field stone in my foundation sweat even when it was -8F outside. Not even the exposed areas above dirt. I'm guessing part of that is due to mass, but it apparently does have some R value to it.
They probably don't sweat because the RH is so low it can't. Our old leaky houses lose so much to air leaks that, for example, my cats glow in the dark as they move in January. And I keep them far away from any electronics.
The photo, directly above, tells you everything about where the lost energy from the boiler goes…………if you are paying attention.
The transfer from the first floor is minimal compared to the above.
Can you name five people who actually accomplish this? 😣
Myself. But I don't go around asking people if they have insulated their basement and I'm not really in the trades, so no, I can't. But any house built with in the last decade should have some amount of basement insulation however if built to code.
As for retrofitting, i think thats more to do with ignorance.
Not sure insulating the walls of a large space you don't use regularly makes good use of materials or funds. Combustion air moves though the space anyway. Another loss. The hope isn't that lost heat would ever be moving up to the 1st floor. That isn't likely to regularly happen but a higher basement temp. will reduce some heat losses coming down from the warmer space above. How about we just say live with the losses whatever they might be and keep it running as well as can be expected. Insulate the dang floor, very little heat if any goes up into the warm space above. Heat will only flow to where it is not.
Sounds reasonable to me, @Teemok
Its not a lot of material or funds? Say you have a square house 24x24 with a 8ft deep basement. It would take 24 sheets of whatever foamboard insulation you choose. If its polyiso that works out to about $1200 before tax. Im including the price because it is right off menards website so not exactly region or a trade secret.
Now polyiso needs an ignition barrier such as drywall. So 52 1x3 furring strips $115. 24 sheets of 1/2" basement board 318$. Of course misc stuff such as drywall screws, mud, tape, tapcons for furing strips, sprayfoam for the joints in the insulation. And your time.
Granted this will not work for all basements. Stone basement? Notta chance. Water pouring in? Nope. Mid century basement with concrete block in good condition? Almost certainly.
For $2k one could go from a cold, damp basement to something that is much easier to heat and keep dry. Run a dehumidifier all summer long? This could pay for its self from that alone.
What's the heatloss difference between 47.8F and 34.3F @ 20F outdoor?
The way that FLIR is setup it makes a 13.6F difference appear huge. Is it?
I actually don't know, and am curious.
My first assumption is if the basement's temperature is 60F which mine usually is and that exposed wall is 2' tall etc, what is going to be the actual decrease in loss and will it ever cover the cost in materials.
Obviously the space would become more comfortable, no argument there. But in my case, that would be moot.
The easiest way to put a number on it is to use a heat loss calculator and punching in the specs of the foundation both with the basement being insulated and uninsulated and look at the difference. I did some years back and the math is what informed me to tackle my basement before the walls or attic in my house. I had always assumed the basement wasn't a large loss because hey its in the ground. Then I ran the numbers and did not get the results I expected. I don't remember the exact numbers but it was eye opening I remember that. About as eye opening as how ineffective replacement windows are vs good low-e triple track storms over original wood windows. Clue: replacement vinyl windows often have a negative ROI, storm windows have a very favorable positive ROI.
This must be qualified. I agree that insulating the basement walls that are in contact with 45F dirt won't provide much benefit for a 50F basement and the cost and effort isn't worthwhile.
However, consider the benefit of insulating the basement wall where it is in contact with 0F (at design) air. The wall has an R value of .8. You're losing 8200 BTU per hour at design (130 sq. ft). This loss is roughly equivalent to the loss by a CI boiler when it is at 180F.
Labor costs are real. If a skilled someone else was paid to do this work around here it would cost well over $3k. but lets go with that and $2k in materials $5K total investment. Lets imagine the boilers stand by losses and pipe loss will be able to heat the ceiling of the newly insulated basement space enough that it now negates any downward heat loss from the space above. How many BTU's/hr have we saved? Rough guess: 25 btu/sqft of 576sqft is 14.4K btu per hour for the whole house on design day. Say 10% loss downward. So it's a 10% savings or 1,440 btu / design day hour or 34,560 btu a design day x 5 months of continuous design days = 5.18 million btu a heating year divide by 100k (a therm) = 52 therms a year at a 20yr average cost of $5 a therm (current is $1.50) = $260 a year saved. There's lot of fudged math towards more savings above. I would think real world would be less, like somewhere between $130 and $260 a year and if gas costs stay lower than proposed, it's even less. 5000/260=19 or 5000/130=38 between 19 to 38 year break even? Cut it in half because you think the math is off: 9.5 to 19 years.
If you want a warmer basement, by all means. The OAT, how many design days, the size of the exposed foundation area, temperature of the 1st floor surface, amount of pipe and insulation, there's a lot of factors. So yes, I can see that insulation of some basements makes sense because you want to lose less heat from the floor above and on terrible lots of loss systems maybe you even heat some of the floor. I'm sure it's done and the owner is happy but that's not the physics. I get the secondary advantages of the boilers waste heat but they can be addressed without boiler or pipe loss and a warmed unused basement.
Typical home 2200 sqft. 55k load met by an 80k input CI boiler @ 81% is 64.4k out with 10% stand by loss is 6,440 btu. Some of that goes to the 50F floor, some out the basement windows if any, some goes through your new insulation, some heats moisture from the floor and some is consumed as combustion air or leaks for air exchange, etc. What's left over to raise the basements ceiling air temp above the floor above's temperature?
I admit, I don't know that answer and don't really want to attempt to figure it out. I do think the the savings numbers are small and payback on saving benefits alone is a long time. Isn't freedom great? We can do as we think is right. I'd insulate the floor hoping to someday to have a more efficient system but if the basement space is ripe for future conversion to living or used space than of course insulating the walls makes sense. in that case I'd do more than just a slap in board strapping job.
You also forgot to account for cooling savings in the summer and dehumidifier savings. Prior to this my dehumidifier ran nonstop 6-7 months of the year. It uses a little under 600watts. Thats easily 2Mw a season for energy. Depending on cost of a kilowatt could be anywhere from $100 to $300 just to keep it at 50%. But wait there's more! Now you need to remove the excess heat it produces.
I cannot express how transformational simply putting some foam board on the foundation was for the air quality and comfort in a 100 year old basement. With or without finishing it into a usable space. And this is absolutely a DIY job. If you have a drill and a box cutter you can install insulation on your basement walls. It was one of those things that I really wish I knew 14 years ago what I know now and would have done first thing before anything else. And if cost is a concern it doesn't have to be polyiso. Any other of the foam board types such as eps, xps work, they just have a lower r per inch.
I mentioned that a stone wall would not be a good candidate for this. Spray foam would be the only potential solution. And thats $$$$$.
I also want to point out that the stick wall is uninsulated except for 1/4" foam board under the vinyl. So 3/4" thick sheetplaster, 2x4, 3/4" "shiplap" sheathing, old cedarshakes, 1/4" styrofoam crap, and finally vinyl siding is the construction of the wall. Maybe r4 or 5 when everything is taken into account. Pump it full of cellulose or that foam usa insulation uses and it would be a noticably larger temperature difference I bet.
Edit: actually there is blown fiberglass up by the second story hall window directly above the door. The attic was insulated some time in the past and they also blew it down through the balloon framed walls as far as it would go. Balloon framing was used from the second floor up to the peak of the roof in the attic on the gable ends. So that 34.2f vs 30f surface temperature might be the difference from no insulation to a fiberglass insulated stick framed wall.
At some risk of asking a question you have already answered… how is the house sill sealed to the foundation?
If you're going where i believe you are, no I'm not too concerned about moisture wicking up into the sill plate. There is sufficient distance between the top of the foundation and grade to keep it dry. It is something I will keep an eye on. If need be I could always dig down and seal the foundation. Which might need to be done at some point anyways. I have no intention of jacking up the house to install a capillary break between the two. I'd rather dig a trench.
But to answer your question the sill plate sits directly on the foundation and I used canned spray foam to seal the joint between the sill, foundation and polyiso. Eventually when I have a few other projects done that are out of the way I'm going to buy one of those kits and spray foam the rim joists all the way around the house from the subfloor to the sill and polyiso.
Basically the terracotta block foundation has been moved outside of the envelope of the structure. The polyiso becomes the edge. The only consideration is how much moisture can get to the sill, and potentially frost freeze cycles since the foundation can now get much colder. But how is this any different than say an unheated garage?
I wasn't worried about moisture — it was infiltration which I was worried by. Seems you've got that under control.
There was a claimed benefit A about basement ci steam boiler losses, then benefits B and C are touted and A is not really addressed.
CI steam boilers have losses that don't contribute to the boilers primary task of heating the conditioned space.
Claim: If you insulate the basement foundation walls the losses are captured and do contribute the primary task.
Secondary claims:
It's not wasted heat if it keeps my pipes from freezing.
It's not wasted heat if it helps with moisture problems.
It's not wasted heat if it makes the basement space more comfortable.
Interior foundation insulation has cooling benefits.
Interior foundation insulation reduces humidity problems.
Interior foundation insulation stops my foundation from glowing so much in exterior thermal pics.
Cats will find the warm spot on the 1st floor.
All True.
It's not wasted heat because boiler losses go into the 1st floor or mitigate substantial losses from the first floor.
Questionable.
I know this is not accurate modeling. I do what I can with what I've got. It might give a glimpse of what's going on or it will manage to get someone more capable to clarify with a convincing proof.
Simplistic math: area x U valve x TD = heat transferred.
65°F average basement, 0°F OAT 2" R13 board on inside of 24x24 foundation wall.
192 sq ft of R13 The 2ft top strip exposed to OAT foundation wall with a 65°F TD might transfers close to a 1000 BTU/hr
576 sq ft of R13. The bottom 6ft with a mix of earth 52°F and chilled from above gradient temperature, avg. 22°F TD might transfers close to 1000 BTU/hr
576 sq ft of un-insulated concrete floor with earth at 52°F and a 9°F TD might transfers 3,836 BTU/hr
Combustion air Loss?
Flue draft loss?
Windows/hatch/door loss?
other?
5,800 btu/hr + (unknowns) could be close to the 80k Ci boiler standby loss. Warmer days than 0°F OAT might raise basement air above 65°F and making it able to start offering heat to the first floor. I don't think it would be substantial but it is possible. Then again, the boiler would fire less under lighter loads and there 'd be less losses to harvest. I don't think the basement floor loss would change much. An other thought: The better sized the boiler is for 0°F design days the less cycling it will do and the less losses there are to harvest. How oversized the boiler is makes a difference in what there is to try to capture.
Knowing what the losses of the specific system are before investing an insulate to capture plan makes good sense. Investments made solely to capture losses from a properly sized ci boiler to reduce first floor heat losses or assist meeting loads is questionable. That said, I welcome good reasoning as to why that's incorrect barring the secondary benefits B,C,D…..
Unless it's a steam boiler with a cycle gard on it.
Then it'll keep cycling and wasting energy. But those claims are also argued.
I'd actually really like to see how much fuel is wasted when a boiler cycles. Especially one that is fully warmed up.
I don't see what you are getting at. If someone has a steam boiler with large standby losses they have only a few options to address the losses.
Rip out the entire steam system and replace it($$$$$)
insulate the basement and bring it into the envelope($$$$)
or just live with the loss.($$$$)
Which one is the most cost effective?
Insulating the basement will absolutely reduce the heat lost through the foundation. To suggest otherwise goes against the laws of physics. It just comes down to the question of if that alone will have a reasonable ROI. Over the life of the boiler maybe not, over the life of the structure absolutely. But to calculate just how quickly it pays for it's self you need to account for all of the variables. Not just cherry pick the boiler.
@JakeCK said: "If someone has a boiler with large stand by losses"
Is a presupposition.
What if they don't?
Insulating solely for loss capture looks a fools task if losses are normal. Live with the losses. Adding fiberglass in the floor is cheap and has a sure return on investment related to the efficiency of existing conditioned space.
This thread started with a what should I do with steam system, where, I didn't understand it had a new working boiler.
After the OP's full remodel the boiler will likely be oversized. Living with those losses in his case is easy as it's a back up system and would rarely be used. The thread then morphed to a insulating basements in general to get many good benefits conversation.
I don't see how the pay back math works related to loss capture only.
@JakeCK said: "Insulating the basement will absolutely reduce the heat lost through the foundation. To suggest otherwise goes against the laws of physics."
This is an odd reply to someone who just before posted a stab at math involving a theorized 24x24 basement with R13 insulation.
I made no such suggestion.
Of course you are correct. The question that begs is how much the slightly higher temperature in the basement reduces the load on the first floor?
Since a CI boiler loses about 10K/hr……….give or take depending on size…………and only when it is at 180F……………..even if all of it benefits the first floor (doubtful)…………….it would be difficult to payback the insulation of the entire basement in your or my lifetime. Remember, when you do the calculation………..to eliminate at least eight months of the calendar year. The boiler doesn't remain at 180F long enough during those eight months to make a difference (the assumption is a typical heating season in the NE……….Minnesota or Alaska are excluded for the purpose of this discusson).
This app is pretty limited, but I'm not getting on the desktop and playing around with the software on that for this debate.
I got a bit different numbers than yours
A simple 24x24x7' box. No windows no doors ceiling factor is 0 because it is at or above the basement temp, uninsulated concrete slab. For the wall it does have an option for a partial above grade block foundation. Just changing what I believe is the u factor from a partially below/above grade bare block wall to something resembling an insulated wall saves 5000btu an hour at 30f outside and 60f inside. My only complaint is that it is saying that bare block wall is over 3r on its own which I question. But since we're comparing the same walls just with more insulation the savings should correlate regardless. In reality due to infiltration, windows, atleast one door and probably multiple flues or atleast multiple appliances going into a single flue the heat loss in a typical basement is going to be much higher even with just a 30f delta. Now lets drop the outside temp around this very simple box to 7f. 12873btuh uninsulated vs 4340btuh insulated.
Now lets look at our typical 2x oversized boiler: 100 year old home that realistically uses about 60k btuh at design but has a boiler that can do more then 2x that. The difference between its IBR and DOE rating is 18000btuh. With the amount of heat that boiler puts out that basement might stay well above 60f. Something I personally experienced last winter. Mine stayed in the 70's, in fact it felt more comfortable in the basement then upstairs even with the temperatures being comparable, especially the dinning room with it's wall of windows.
Ill agree in a perfect world where everything was sized right, standby losses should be minimized. But we don't live in a perfect world. Most heating systems are grossly oversized. Most of these people are not going to replace their heating systems until it dies. Guess what? Most of these people will hire the lowest bid and will probably be sold to much boiler or furnace again as well.
All The comparing of apples and oranges aside, I think you just agreed. Your 1st floor doesn't see much if anything from your basement that is the same temperature. If we 8x oversize the boiler and use big waste heat figures put into the basement maybe we could show it could heat the whole 1st floor.
Math assumptions aside.
The theory is the boilers waste heat W (whatever it is) is greater than the newly insulated basement's heat loss L (whatever it is).
Result case 1: Boiler losses cause the basement to warm enough to 100% prevent or dramatically reduce the 1st floor's downward heat loss.
Result case 2: Boiler losses cause the basement to warm enough to offer heat up to the 1st floor.
You can play with all kinds of combinations of boiler waste W's and basement loss L's to get the result you want.
I think result 1 is possible and would make the 1st floor's downward heat loss effectively zero. If that downward loss prevented is near 10% of the house's total load, it takes a very long time to pay off the insulation project.
I think result 2 is unlikely except for outlier rare high boiler loss combined with low basement loss scenarios.
In the result 2 case mitigating boiler losses directly with boiler and pipe insulation,whatever is clever, might be better money spent given that a warm basement is of no interest.
I've said before, if a warm basement is desired, insulation is a good idea but as a means of directing typical boiler losses though the 1st floor, not so much.
That's my opinion and it's worth what you paid for it. The truth of the matter may fall outside of both of our figurings. That's ok.
I'm not invested in any specific case scenario. It's the theory that interests me and what conditions might be needed to make pay back reasonable so that if I confront a case I have a sense of where the go no go lines is.
I have some questions:
You have a single "wall factor". This wall factor is not identical for the wall in contact with the dirt versus the wall in contact with the air. This tends to invalidate the comparison as the wall in contact with the air is where most of the loss occurs.
You have a "floor factor" of .81 with an indoor temp of 60F and an outdoor temp of 30F. This is clearly incorrect as the "outdoor temp" of the floor is the temperature of the dirt below the floor…………estimated at 50F.
The app has settings for both of those scenarios. You just dont see them on that screen. When selecting the options for the floor there is one for uninsulated concrete. I can only imagine it makes an assumption that it is 50f dirt. Same is true for the wall. There is an option for a block wall that is partial below grade.
I did make a mistake, i selected the wrong one for the floor. At grade no insulation, instead of below grade. It decreased btuh by ~500btuh in both cases.
I would argue depending on the insulation of the rest of the house the loses to the basement will be much greater than 10%. Add just a few inches of loose fill fiberglass to the attic and suddenly you'll lose more btu's to the ground then to the attic. It's one of the reasons the code is now mandating continuous insulation as a percentage or all of it. Sure you might be r20 or more on a 2x6 wall but that relatively small surface area of the framing becomes the dominant loss. Likewise you could have r60 ceilings and r30 walls but if the basement is cold you're going to lose everything there. And with 2x10 joists you could shove r30 between them but you still have upwards of 20% of the surface area at whatever the value is per inch of that wood.
Now since so many are convinced insulating the floor is the best option lets pan that out. 500$ for the fiberglass to do that scenario. And since you insisted including labor costs for the polyiso on the foundation, a job any competent homeowner can do themselves, include it here as well. And make sure to include the cost of air sealing every penetration going into the subfloor, and insulating around the basement door and the stairwell as well, which at the very least is going to include drilling into finished walls and patching.
It is much more difficult to get a good seal on irregular surfaces with lots of penetrations such as a ceiling or attic floor especially one that has an entire stairwell going through it. It is why CI at the envelope boundary performs so more better that fluffy stuff shoved in a framing cavity. Will the saving of the boiler pay for it all? yes. When? Maybe in 10 years maybe 100, it depends. But that is far drom the only benefit.
One other point I want to make is we're using a simple 24x24 box as the example. What happens when the box gets larger. Much larger. The surface area of the foundation with 7ft ceilings is 672sq ft, the surface area of the ceiling is 576sq ft. A 36x36' box is 1296 for the ceiling, but the foundation is now only 1008sq ft. ;). See how the math is starting to tilt the other way?
- 87K THE MAIN WALL
- 116 Chimneys & Flues
- 109 Geothermal
- 985 Plumbing
- 389 Solar