Main vent capacity vs tap size
Wcurtis
Wcurtis Member Posts: 132
if an additional main tap is added, does this allow more venting capacity because I feel limited due to a single tap.
62' of 2.5" pipe, currently have 1 B@J Bigmouth and system appears to work fine.
Tried 2 Bigmouths then 1 Bigmouth and 1Hoffman 75 with no improvements on either combination.
    Jamie Hall Member Posts: 27,313
    What pressure are you seeing at the boiler as the system is coming up to steaming and filling the system? It's very likely that one Big Mouth is ample, but the way to check is to look at the pressure. If it rises very little, or comes up no a few ounces and then sits there until the system is pretty well full of steam — all the radiators hot — your venting is fine.
    Mad Dog_2
  • JUGHNE
    JUGHNE Member Posts: 11,547
    What is the pipe size tap is the vent connected to? 3/4…1/2 etc?
    Steamhead Member Posts: 18,455
    And, how long between the steam entering the main at the boiler end, and when it reaches the vent?
    Consulting
    Mad Dog_2
  • Wcurtis
    3/4" tap
  • Wcurtis
    pipe size and length was used to determine vent from "Greening Steam" main vent chart for Hoffman 75 and B@J chart for Bigmouth..all based on 1oz column in each chart.
    3/4 inch tap is more than enough!
    Mad Dog_2
  • Wcurtis
    Appreciate the feedback, if I add an additional 3/4" tap will this increase the venting capability?
    No, You could put a very impressive antler on that singe tap and still do fine.
  • Neild5
    Neild5 Member Posts: 203
    3/4 tap can easily support 2 Big Mouths.