if an additional main tap is added, does this allow more venting capacity because I feel limited due to a single tap.

62' of 2.5" pipe, currently have 1 B@J Bigmouth and system appears to work fine.

Tried 2 Bigmouths then 1 Bigmouth and 1Hoffman 75 with no improvements on either combination.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,859

    What pressure are you seeing at the boiler as the system is coming up to steaming and filling the system? It's very likely that one Big Mouth is ample, but the way to check is to look at the pressure. If it rises very little, or comes up no a few ounces and then sits there until the system is pretty well full of steam — all the radiators hot — your venting is fine.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2
  • JUGHNE
    JUGHNE Member Posts: 11,279

    What is the pipe size tap is the vent connected to? 3/4…1/2 etc?

  • Steamhead
    Steamhead Member Posts: 17,387

    And, how long between the steam entering the main at the boiler end, and when it reaches the vent?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • Wcurtis
    Wcurtis Member Posts: 71

    3/4" tap

  • Wcurtis
    Wcurtis Member Posts: 71

    pipe size and length was used to determine vent from "Greening Steam" main vent chart for Hoffman 75 and B@J chart for Bigmouth..all based on 1oz column in each chart.

  • Jamie Hall
    Jamie Hall Member Posts: 24,859

    3/4 inch tap is more than enough!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2
  • Wcurtis
    Wcurtis Member Posts: 71

    Appreciate the feedback, if I add an additional 3/4" tap will this increase the venting capability?

  • Jamie Hall
    Jamie Hall Member Posts: 24,859

    No, You could put a very impressive antler on that singe tap and still do fine.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Neild5
    Neild5 Member Posts: 181

    3/4 tap can easily support 2 Big Mouths.