RC & RH at T-Stat
Options

Servicewiz_3
Member Posts: 64
I have recently viewed a U-tube tutorial on the "C" wire for the New Honeywell Resideo thermostat. I had always been told, if the stat subbase uses both RC & RH, the transformers must be placed in phase to be used together.
Can this rule also apply to this new stat?
Thanks in advance for any help!
0
Comments
-
Yes it does.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0