RC & RH at T-Stat

I have recently viewed a U-tube tutorial on the "C" wire for the New Honeywell Resideo thermostat. I had always been told, if the stat subbase uses both RC & RH, the transformers must be placed in phase to be used together.

Can this rule also apply to this new stat?

Thanks in advance for any help!

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,696

    Yes it does.