Beckett Honeywell r7184b
binlon
binlon Member Posts: 1
How do I check the unit is getting electrical power? No hot water and no green light on ! Please advise
  • Big Ed_4
    Big Ed_4 Member Posts: 3,474
    edited July 2024
    You need a voltage meter , work back until you find break .. But now ..Check the emergency switch on the top of the stairs …
    Jamie Hall Member Posts: 27,166
    And the relevant fuse or circuit breaker…
    Steamhead Member Posts: 18,361
    Or, it might be by the outside basement entrance, possibly on the ceiling. Both locations were approved back in the day.
    Consulting
    EdTheHeaterMan Member Posts: 11,906
    R7184B primary control with 15 second safety timing can be connected to replace a 3 wire primary control or it can be connected differently with separate power to L1 (power) and Limit (also power). Depending on how the control is connected ( or wired) it may be normal to have no power the the control. You need to see what limit control you are using. That may be the place where the power to the L7184B control is interrupted. Look for ~120V electricity between B1 and B2 on the limit / aquastat control
    Post a photo of the controls on your heating system with the covers off of the controls from 5 to 6 feet away and some close up shots or the controls