Beckett Honeywell r7184b

binlon
binlon Member Posts: 1

How do I check the unit is getting electrical power? No hot water and no green light on ! Please advise

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,017
    edited July 21

    You need a voltage meter , work back until you find break .. But now ..Check the emergency switch on the top of the stairs …

    There was an error rendering this rich post.

  • Jamie Hall
    Jamie Hall Member Posts: 24,838

    And the relevant fuse or circuit breaker…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 17,376

    Or, it might be by the outside basement entrance, possibly on the ceiling. Both locations were approved back in the day.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378

    R7184B primary control with 15 second safety timing can be connected to replace a 3 wire primary control or it can be connected differently with separate power to L1 (power) and Limit (also power). Depending on how the control is connected ( or wired) it may be normal to have no power the the control. You need to see what limit control you are using. That may be the place where the power to the L7184B control is interrupted. Look for ~120V electricity between B1 and B2 on the limit / aquastat control

    Post a photo of the controls on your heating system with the covers off of the controls from 5 to 6 feet away and some close up shots or the controls

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?