Nti boiler too much psi
edit: I may be wrong
Can you post your NTI model number0 -
can you take a picture of the install as well0
I don’t have a before pick still looking. For one. We used to have baseboard heat all around the house. We removed it all and closed everything up
thanks everyone
Im a little confused. Did you just abandon the heating side of the boiler and just are using the combi part of the boiler? If the boiler pressure is going up, you may have a bad plate heat exchanger. If it has a tiny hole, you are putting city water pressure in the boiler. Boiler pressure is much lower than city or well water so naturally the boiler pressur will rise… remember at 30 psi, the relief will dump. I assume that you checked and set the boiler pressure with the PRV? We get so many calls for boiler relief leaks or high boiler pressure. I tell the men its always one of 3 things. Bad fill valve that is over filling, water logged expansion tank, or bad relief from people yanking on the relief lever everytime they walk by it. Hope that helps.
You still need an expansion tank on the heating side of the boiler, looks like you put one on the domestic piping, but that tank never sees the boiler water.
You need 2 relief valves total (one for DHW, and one for boiler), and at least an expansion tank on the boiler side, preferred to have one on the DHW side as well but not always necessary
you need these things whether or not you are using the boiler for space heating, it is still a pressure vessel, and it is still being used to heat your water, both the DHW and boiler side are used to make DHW
It's a good thing these boilers have built in safeties
And I hope that you didn't drain the heating side of the system. I the heating side heat exchanger is dry, it will die a nasty and early death — if it hasn't already. Not sure quite how I would handle that situation, since the heat exchanger must have water in it — and that water must take the heat away from it, even when only the domestic side is calling.
hmm…