Steam pipe style convectors
todd_ecr
todd_ecr Member Posts: 92
I’m trying to size a boiler for a church in upstate NY.  Would anyone know the EDR for something like this?  The individual pipes are 1-1/2”.  They are around 60’ long on each side
mattmia2Intplm.
  • KC_Jones
    KC_Jones Member Posts: 5,936
    Are they 1.5" SCH 40 pipe, or actually 1.5" OD?
    1.5" SCH 40 pipe would be 0.497 sq ft EDR per 1' of pipe
    If it's actually 1.5" OD that would be 0.393 sq fr EDR per 1' of pipe
    2014 Weil Mclain EG-40
    Intplm.
    Steamhead Member Posts: 18,548
    That's a pipe-coil radiator. I know there are charts for these but didn't see them in the site's Heating Museum. I'll keep looking, as I'm sure all the Wall regulars will B)
    Consulting
  • guzzinerd
    guzzinerd Member Posts: 460
    That's amazing
    Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,566
    Dan's Books have all these formulae. Start your essential library ✨️ today!  Mad Dog 🐕
    mattmia2Intplm.
  • ChrisJ
    ChrisJ Member Posts: 17,436
    So,
    Roughly 180sqft EDR?
    ethicalpaul Member Posts: 8,881
    I'd like to see an IR video of that heating up. I wonder if the whole thing heats up or just one or two of the pipes
    CLamb
  • KC_Jones
    So,
    If each pipe is 60', and it looks like 6 of them, then yes 180 should be the number.
    mattmia2 Member Posts: 16,940
    why are there vents everywhere if it is 2 pipe? or is it 1 pipe with a condensate return below the water line or to a water seal or something like that?
    It also really should only need one big vent down where that ell and nipple is at the bottom.
    Looks like a 2-pipe air-vent system- pre-Vapor.
    Consulting
  • dabrakeman
    dabrakeman Member Posts: 1,017
    LAOSH (page 123) says for the 1 1/2" pipe Direct Pipe Coils a 6 row 60' would be 3.3*60=198sqft.
    bburd
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,363
    Here you go. As seen in The Golden Rules of Hydronic Heating.
    President
    HeatingHelp.com
    ScottSecordelcrossvPC7060Intplm.
  • Kickstand55
    Kickstand55 Member Posts: 115
    I've seen this at a Church in Manchester, NH. Much of the pipes were patched with clamps and rubber. The building was built in the late 1800's.
    I actually proposed a replacement boiler and to replace the piping or new radiation. Old steam traps abound with nicely painted in silver. Not a scratch on the bolts. There also exists 2 zone actuators and a hot waterside arm heater for baseboard heat. Someone removed 1 section from the boiler. Yup, there was a hole in it. Much water hammer.
    I presented my case and it was denied. Now there is a new boiler. More water hammer than before.
    You get what you pay for.