Hello - I have a very old but working Hydrotherm gas/hot water boiler (HC 125). The relay is acting irregular and I am looking to replace it. The relay is electrozone RB-4A and is no longer available. I believe the output to the thermostat is 20 V. DC.
At this point, the boiler is 1 zone, 1 thermostat (the zone valves went bad a while back and I removed the internal switch cylinder). The house is fairly small and 1 zone heating works fine.
Can someone recommend a relay that would replace the Electrozone and provide 1 zone heating? The wiring on the current relay looks fairly straight forward.
Thanks!
    EdTheHeaterMan Member Posts: 8,046
    What controls the gas valve? Is it an end switch off of the Electrozone relay? If yes it is easy.
    If you are only using one thermostat, you just need to bypass the end switch and wire directly to the limit devices. basically connect the thermostat to the wires you remove from the end switch.
    Send a photo of the inside wiring connections of the Electrozone relay. Also send a photo for the boiler from far enough back to see that other controls. Then I can verify the vest step forward
  • Soundart
    Soundart Member Posts: 6
    I'll send a photo of the whole shebang later. Thanks.
  • Soundart
    HVACNUT Member Posts: 5,860
    I don't know of any D.C. controlled switching relay that isn't a lot more than you need. Is there a Radio Shack around?
    I'm sure it would be easier to convert to 24 VAC controls.
    Let's see the zone valve. I see a piece.
    pecmsg Member Posts: 4,882
    Not for at least 10 years!
  • Soundart
    The zone valves are no longer functional and are permanently in the open position I am a novice and may be mistaken, but I think I need a relay that responds to the thermostat and will turn on the circulating motor and activate the burner until it reaches temperature. Since the zone valves are deactivated, is the 20 V DC output of any significance? Again, thanks for help!
    If the zone valves are constantly open and the thermostats can handle AC switching, then a Taco SR501 or equivalent will work. TT on boiler is X1,X2.
    SteveSan
  • Soundart
    my current thermostat is Honeywell T822A. Will that be compatible?
    Post a pic. I believe they are a mercury thermostat that mounts vertically in a Gem box. Should be ok.
  • MikeAmann
    MikeAmann Member Posts: 998
    Even if you did have to change the thermostat, they're cheap.
    edited February 27
    The T822A thermostat is fine for the 24 VAC control.
    I placed the Electrozone numbers on the diagram in Blue
    Notice how terminal H and 3 on the Taco SR501 are equal to terminal 1 on the Electrozone. because there is a Jumper between H an 3 on the Taco
    This is the part you want to order
    https://www.supplyhouse.com/Taco-SR501-4-1-Zone-Switching-Relay
  • Soundart
    Thanks so much to you all. I am hoping I can nurse the current relay until spring and then change over to the Taco. Seems very clear and not too difficult.