replacement for Electrozone relay
Soundart
Member Posts: 8
Hello - I have a very old but working Hydrotherm gas/hot water boiler (HC 125). The relay is acting irregular and I am looking to replace it. The relay is electrozone RB-4A and is no longer available. I believe the output to the thermostat is 20 V. DC.
At this point, the boiler is 1 zone, 1 thermostat (the zone valves went bad a while back and I removed the internal switch cylinder). The house is fairly small and 1 zone heating works fine.
Can someone recommend a relay that would replace the Electrozone and provide 1 zone heating? The wiring on the current relay looks fairly straight forward.
Thanks!
At this point, the boiler is 1 zone, 1 thermostat (the zone valves went bad a while back and I removed the internal switch cylinder). The house is fairly small and 1 zone heating works fine.
Can someone recommend a relay that would replace the Electrozone and provide 1 zone heating? The wiring on the current relay looks fairly straight forward.
Thanks!
0
Comments
-
What controls the gas valve? Is it an end switch off of the Electrozone relay? If yes it is easy.
If you are only using one thermostat, you just need to bypass the end switch and wire directly to the limit devices. basically connect the thermostat to the wires you remove from the end switch.
Send a photo of the inside wiring connections of the Electrozone relay. Also send a photo for the boiler from far enough back to see that other controls. Then I can verify the vest step forward
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I'll send a photo of the whole shebang later. Thanks.0 -
0 -
I don't know of any D.C. controlled switching relay that isn't a lot more than you need. Is there a Radio Shack around?
I'm sure it would be easier to convert to 24 VAC controls.
Let's see the zone valve. I see a piece.0 -
The zone valves are no longer functional and are permanently in the open position I am a novice and may be mistaken, but I think I need a relay that responds to the thermostat and will turn on the circulating motor and activate the burner until it reaches temperature. Since the zone valves are deactivated, is the 20 V DC output of any significance? Again, thanks for help!0
-
-
my current thermostat is Honeywell T822A. Will that be compatible?0
-
Even if you did have to change the thermostat, they're cheap.0
-
The T822A thermostat is fine for the 24 VAC control.
I placed the Electrozone numbers on the diagram in Blue
Notice how terminal H and 3 on the Taco SR501 are equal to terminal 1 on the Electrozone. because there is a Jumper between H an 3 on the Taco
This is the part you want to order
https://www.supplyhouse.com/Taco-SR501-4-1-Zone-Switching-RelayEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
-
Looking at that control, it looks like a selenium rectifier on it (the green thing). That stuff is fairly not-very-good for you, & it should probably go to a hazardous waste drop-off point.
0 -
Never heard of it. Wiki says
During catastrophic failure they produce significant quantities of malodorous and highly toxic hydrogen selenide.
Smells that make you go hmmm
30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
I will do that. Thanks.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements