Steam Radiators double trapped question
Chuck_17
Member Posts: 148
See attached.
Will this work?
1. Radiators with thermostatic traps - condensate connected to an F&T trap?
2. Two radiators condensate connected together between the above traps?
Will this work?
And why on earth would you want to do that? If the thermostatic traps are functioning as they should, there will never be anything except air and condensate in the return. If they aren't, adding an F&T somewhere isn't going to help anything. Further, most F&T traps are really lousy vents, and you want the return to have the maximum venting possible.
In short, poor idea. Don't do it.Br. Jamie, osb
To clarify, this is an existing recently installed. Radiators, TCV, T trap all new connected to an existing F&T trap.
The questions is - should the F&T trap be removed?0 -
Yes if all that is feeding the F & T is the two rads remove the f & T. If there are other pipes feeding the inlet of the f& T that are not trapped the connect the outlet of the thermostatic traps downstream of the f&t. That is assuming the condensate return is above the boiler water line and is a dry return. If it's a wet return you need vents to get rid of the air.0
You would connect the drain from the thermostatic traps after the f&t on the condensate return, downstream of the f&t.0
Thanks for the replies.
There is nothing else on the F&T.
Do you think it would work with the F&T left in place?
It is operating now but it has not been that cold.0