HTP Boiler short cycle
Is this new behavior?
If it is there might be a strainer in there, make sure it is clear.
If not the setpoint may be too high, it will try to get to the setpoint as fast as possible, if the system can't get rid of that much heat it may shout down. You can limit the firing rate, if there isn't about 50,000 btu/hr of attached radiation I would turn the firing rate down to match what is attached to it.0 -
It has honestly acted like this intermittently since install in 2017. There were a few times when it definitely had air in the system because it would boil very quickly and shut down with the high water temp error. The heated space is about 1500 sq feet. I will turn down the set point 5 degrees and see if I get that low fire maintaining. I’ve had enough issues with it over the past couple of years that I honestly don’t know what normal looks like. I have flushed the boiler a few times in the past few days so I don’t think there’s any blockages.
if there is a strainer you have to take it out and clean it. But it sounds more like you need to go in the installer menu and set the max firing rate to maybe 50% or 75% so it doesn't put heat in to the system so fast.0
I’ll dig into the manual and see where that setting is. I appreciate the insight. Where would the strainer be located if it had one?0
You'll have to look in the parts diagram in the manual and see if there is one. i have a uft-100 but i've never needed to know if it has a strainer.0
The manual shows I can adjust combustion rate. Is that the same as firing rate?0
There’s no strainer on that boiler, but lowering the firing rate may help.
It appears that you only have 3/4” piping connected to the boiler. If so, that’s only good for 40k btus.What type of radiation do you have? Fin tube baseboards? If so, measure the linear feet of ELEMENTS (not the enclosure) that you have and multiply that by 500 to get the total btu output. It’s probably less than 50k.
The firing rate can be limited in the control. There’s also a step modulation function which should be turned on to help with this issue.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.3 -
Yes, fin tube baseboards. I’ll give them a measure. There’s a combustion rate setting in the controls. Is that the same as firing rate?0
After doing that calculation, I come up with 27,800. For what it’s worth, the second zone only calls for heat about 75% of the time compared to the first zone.0
Zone 1 is about 32.6 lf
zone 2 is about 22.8 lf0 -
joncroteau said:Yes, fin tube baseboards. I’ll give them a measure. There’s a combustion rate setting in the controls. Is that the same as firing rate?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
If it's a setting issue, you will need to get the settings right with any new boiler as well, so a new boiler doesn't seem like the solution to me, based on what you've posted.joncroteau said:I think I’m going to start to price out a new system altogether. This HTP has been problematic since install.
3 -
joncroteau said:I think I’m going to start to price out a new system altogether. This HTP has been problematic since install.5
I have a uft-100 that I have had for about 5 years now. The only issues I have had with it are an issue with some off gassing from the insulation around the HX until I ran it up to 180 or so once and a very occasional stored error code about the fan speed that doesn't cause any noticeable issue other than the stored code. I think it is some sort of firmware bug involving power up or maybe momentary power interruptions. @ironman has installed many of these and had little problem with them.0
The problem is NOT the boiler. It’s the fact that the installation wasn’t done correctly.
Make the suggested parameter adjustments and your issue should be mitigated.
If necessary, add a buffer tank as Ed suggested.
As mentioned, any mod/con is gonna have the same issues unless it’s setup correctly.Bob Boan
Ironman said:The problem is NOT the boiler. It’s the fact that the installation wasn’t done correctly.
As mentioned, any mod/con is gonna have the same issues unless it’s setup correctly.0 -
when was it last checked with a combustion analyzer?0
With the house "cold" ie 61F - 69F; the boiler had a "load" more in line with how it's currently setup - This proves that adjusting firing rate and modulation will help match the boiler to the system - low mass wall hung boilers are great; and most come with wide programming functionality - it's up to the installer to understand that and fine tune those parameters.2
mattmia2 said:when was it last checked with a combustion analyzer?0
joncroteau said:mattmia2 said:when was it last checked with a combustion analyzer?mattmia2 said:when was it last checked with a combustion analyzer?0
joncroteau said:
It hasn’t ever. I’m setting that up with my local hvac company. The boiler also throws ‘no ignition’ codes so I will have them check the pressure as well.joncroteau said:mattmia2 said:when was it last checked with a combustion analyzer?
Any idea what the normal parameters of the combustion test would be?mattmia2 said:when was it last checked with a combustion analyzer?
it is in the manual
it must be set up with a combustion analyzer when it is installed. if the combustion isn't adjusted right it is likely to not ignite sometimes. if it has been running for years like that it likely needs soot cleaned out of it too2 -
This was in low fire. Tech checked on high fire and said it was right in the range. He also dialed the gas pressure up to 10.9. It was 9.56 when he started. Also checked the inducer and that was clean and in tact.0
is this propane?
there is a min spec for the propane pressure and i think it is a lot less than that so adjusting the house regulator doesn't seem necessary.
if it is lpg something could be happening with your system that it is not supplying enough pressure after an extended draw or in very cold weather.0 -
Yes, Propane. He adjusted this on the gas valve on the boiler. It’s relatively warm here for this time of year. Not entirely sure where to go next.0
The pressure is just measured at the boiler, if it needed to be changed that would be at the house regulator. The adjustment for the mixture is made at the gas valve.
The procedure is on page 47.
https://www.htproducts.com/literature/lp-542.pdf
Moisture in the propane or a low or too small for the size of the draw tank or ice plugging the regulator vent or piping that is too small for all of the loads can cause the propane supply pressure to drop.
Has it been opened and cleaned regularly?
I think there is also a recall on some versions with a plastic flap in the exhaust that could break loose.0 -
mattmia2 said:The pressure is just measured at the boiler, if it needed to be changed that would be at the house regulator. The adjustment for the mixture is made at the gas valve. The procedure is on page 47. https://www.htproducts.com/literature/lp-542.pdf Moisture in the propane or a low or too small for the size of the draw tank or ice plugging the regulator vent or piping that is too small for all of the loads can cause the propane supply pressure to drop. Has it been opened and cleaned regularly? I think there is also a recall on some versions with a plastic flap in the exhaust that could break loose.0
The vent can get blocked with snow or ice if it isn't arranged so it is protected.0
When the boiler was originally designed and initially delivered in 2015, it had serious issues with the control logic. The boiler could not modulate quickly enough before it reached +5F. over limit. Then it would shutdown on limit and restart about one minute later.joncroteau said:It has honestly acted like this intermittently since install in 2017.
HTP made several iterations of that control over the two years between 2015 and 2017.
When done, the boiler could respond properly to an instantaneous closure of two zones (out of a total of three) and it would NOT shutdown on limit. HTP decreased the response time for modulation and also increased the the margin to +12F over setpoint before a shutdown occurred.
The final result was truly excellent from the original starting point.
Sadly, most installations of this boiler in that time frame will suffer from the poor control logic and none of the installers can do much about it.
You can mitigate the issue to some degree by reducing the CH heating capacity. This is parameter 18:cb on the display. If you can heat the building with 40K BTU's (likely) set the parameter at 55. It's much easier for the boiler to modulate down from 40K then from it's maximum (72K). Step modulation (37:CM) will not help with this issue.
However, understand that this approach will severely limit your capability of recovery if you are inclined to reduce the building temperature overnight.
If you were to replace the control board, all issues would disappear.
2 -
When the boiler was originally designed and initially delivered in 2015, it had serious issues with the control logic. The boiler could not modulate quickly enough before it reached +5F. over limit. Then it would shutdown on limit and restart about one minute later. HTP made several iterations of that control over the two years between 2015 and 2017. When done, the boiler could respond properly to an instantaneous closure of two zones (out of a total of three) and it would NOT shutdown on limit. HTP decreased the response time for modulation and also increased the the margin to +12F over setpoint before a shutdown occurred. The final result was truly excellent from the original starting point. Sadly, most installations of this boiler in that time frame will suffer from the poor control logic and none of the installers can do much about it. You can mitigate the issue to some degree by reducing the CH heating capacity. This is parameter 18:cb on the display. If you can heat the building with 40K BTU's (likely) set the parameter at 55. It's much easier for the boiler to modulate down from 40K then from it's maximum (72K). However, understand that this approach will severely limit your capability of recovery if you are inclined to reduce the building temperature overnight. If you were to replace the control board, all issues would disappear.0 -
The step modulation will likely not help your issue and will delay the response to the building. You want the boiler to immediately go to whatever level is necessary to heat the building on the design day. If your heatloss is 40K, that's all the output the boiler requires. The CH limit will accomplish this.
I believe you will have quite a bit of success with a CH limit of 55 (assuming a 40K heatloss).
I guarantee that you will have success with a CH limit of 45. HOWEVER, you MIGHT need to raise it if you get near the design day. Remember I am making an assumption on your heatloss. If you know what you have you can calculate the CH limit appropriately. Figure the output of the boiler is 70K and calculate based upon your own heatloss for the building.1 -
hi- back again with more questions on this system. The heating season is here and I’ve set the combustion rate to 50%. I do get much longer run times on this setting. Do you happen to know if this would ‘override’ step modulation if I have that turned on? Logic tells me that it would.
If you are satisfied with 50%, you don't need step modulation. Just disable it. I tend to doubt that it would override the the step although the step is somewhat meaningless if you are limiting CH to 50%.
As I mentioned, with a proper control board, you don't need a limit and you don't need step. These are bandaids if the control cannot modulate fast enough to keep up with the change in return temperature (the boiler shuts down on limit).'
The new board on the one system I installed………….refined after two years………….will allow me to shutdown two of the three zones instantly as a test, and the boiler will NOT shutdown on HL. HTP refined the control significantly over the first two years and the result is perfect. Sadly most folks do not realize they are struggling with an early design of the control.
Thank you. I watched the boiler maintain 165f for over 1.5 hours yesterday (i set the heat call to 75f just to see how long it would run and if it would get up to temp) From what I have seen, a new control board isn’t terribly pricey. That is my next step. If I order a new board, do I need to specify that I want the upgraded version, or is that the only version available?
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 980 Plumbing