Steam Valve
mmc239
Member Posts: 94
I have a steam shut off valve on my steam baseboard that has a broken knob. Is it ok to use a plier to turn the stem to open and close it?
Sure, until it gets rounded out and is useless.
Knobs are still available.
Proper Open-end wrench will work.
I've used my refrigeration ratchet wrench when needed.0 -
Is this one pipe or two pipe steam?
If one pipe that is a service valve only, not for regulating the heat; it must be either fully open or fully closed. Heat is regulated by controlling the air vent at the other end of the rad.
If this is a two pipe system that may be a throttling valve, but it won't last long if adjusted frequently.—
Bburd0 -
It is a one pipe. I don’t think it is fully open. Just trying to get it that way.0
What problem are you having with the performance of the system that leads you to want to mess with the valve?—
Bburd0 -
I get a lot of banging and water spitting out of air vent. Makes believe it’s not draining back to boiler correctly.0
Baseboard can be problematic on steam systems.
The easiest thing to check is the pitch; the baseboard should pitch toward the supply valve so condensate can run back that way.
A slower vent may help by reducing the rated which the baseboard produces condensate.
The supply valve needs to be fully open. Sometimes the internal parts fail and block the flow of steam and/or return of condensate causing the symptoms you Have. You would have to look inside the valve by removing the bonnet or disconnecting it from the baseboard to check, which would have to be done when the boiler is off and not likely to be restarted soon.—
Bburd0 -
Does anyone know what size this shut off valve is and how difficult it is to replace?0
hope this helps with the size.
As far as how easy it is to take apart to replace... It looks like it was done in the past by the looks of that wall behind the cover.
You will need to take the SPUD off also, unless you can find the identical valve (not Likely) the union nut threads will not match up with the new valve.
2 -
My guess is that you have some commercial baseboard radiators with 1-1/4" steel IPS with fins. So that valve is probably 1-1/4"
\https://www.supplyhouse.com/Bluefin-RVST125-1-1-4-FIP-x-Male-Union-Steam-Angle-Radiator-Valve and you will want to get this wrench https://www.supplyhouse.com/Bluefin-RVSW-2-Radiator-Valve-Spud-Wrench?_br_psugg_q=radiator+spud+wrenchEdward Young Retired
EBEBRATT-Ed said:
@EdTheHeaterMan
What's wrong ? X-ray vision not working today?
Some days you get the bear, some days the bear gets you!
I think it is the same size at this other comment https://forum.heatinghelp.com/discussion/195868/steam-valve
What is the chance that there are two people with the same exact valve?
I hope this guy has the same sense of humor
@mmc239, I've merged your duplicate posts into one here to prevent confusion. Thanks.
President
HeatingHelp.com1
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam