Hydronic Floor hot spot 110F surface
Terl22
Member Posts: 5
Just purchased a house this summer with hydronic radiant heating on the main floor. It seems to be working fine but I’m still trying to make sense of it. Tonight I noticed a hot spot in one area with surface temp of ~110 with the rest of the floor around 85-90F. Attached are some pictures of the setup. Any advice or guidance is greatly appreciated
Pretty weird if they're all coming off the same tempered loop. Show the boiler piping.
Pictures attached. From what I understand. Anything without a zone valve on the manifold will heat whenever the indoor sensor is not at set point and the others will open based on the wall thermostats
You find A hot spot? Do you have an autofill on that system? I'm suspicious of a leak.Br. Jamie, osb
Yes there is an autofill. I checked the basement below the hot spot and no sign of moisture0
Possibly tube bunching where they eminate from. Looks like someone tried to do a quasi European design (constant circ, outdoor reset). Without seeing an IR picture, its hard to say. Got FLIR?
Any DHW lines in that area?Bob "hot rod" Rohr
If you look at the first picture, there are zones labeled Great Room #1 and Great room #2. Under this setup will Great room #1 get constant flow based on the indoor sensor?Mark Eatherton said:Possibly tube bunching where they eminate from. Looks like someone tried to do a quasi European design (constant circ, outdoor reset). Without seeing an IR picture, its hard to say. Got FLIR?