Hydronic Floor hot spot 110F surface
Terl22
Terl22 Member Posts: 5
Just purchased a house this summer with hydronic radiant heating on the main floor. It seems to be working fine but I’m still trying to make sense of it. Tonight I noticed a hot spot in one area with surface temp of ~110 with the rest of the floor around 85-90F. Attached are some pictures of the setup. Any advice or guidance is greatly appreciated
    HVACNUT Member Posts: 7,443
    Pretty weird if they're all coming off the same tempered loop. Show the boiler piping.
  • Terl22
    Pictures attached. From what I understand. Anything without a zone valve on the manifold will heat whenever the indoor sensor is not at set point and the others will open based on the wall thermostats
    Jamie Hall Member Posts: 27,367
    You find A hot spot? Do you have an autofill on that system? I'm suspicious of a leak.
  • Terl22
    Yes there is an autofill. I checked the basement below the hot spot and no sign of moisture
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,874
    Possibly tube bunching where they eminate from. Looks like someone tried to do a quasi European design (constant circ, outdoor reset). Without seeing an IR picture, its hard to say. Got FLIR?
    hot_rod Member Posts: 27,452
    Any DHW lines in that area?
  • Terl22
    Nope, this is in the middle of the room
  • Terl22
    If you look at the first picture, there are zones labeled Great Room #1 and Great room #2. Under this setup will Great room #1 get constant flow based on the indoor sensor?