Modulating pressure issue
Acon12
Acon12 Member Posts: 3
I have a low pressure Burnham 3 pass firetube stream boiler with a Gordon-Pratt 12S burner. I adjusted the modulating pressure control to modulate the boiler around 4 psi (with additive diff) with the operating control set a 6. I can see the boiler gets to low fire in the modulation, but the boiler still trips on operating pressure of 6 and begins another cycle. I would like to run longer cycles and have adjusted the mod pressure down at times to see if it holds a consistent pressure, but it continues to top out. Any idea why that is?
  • ratio
    ratio Member Posts: 4,234
    If the pressure is rising, you're making more steam than you're condensing. What application?
  • Acon12
    I’m overseeing an old elementary school. 1920s build and 65,000 sq ft. There’s about 20 radiators throughout and I have a little over a dozen reheat boxes that heats air pushed into the classrooms. Theres a couple preheat coils if needed. The strange thing is, I have twin boilers, and my boiler 1 runs and modulates with little to no cycling. They share the same one pipe system
  • bburd
    bburd Member Posts: 1,303
    It sounds like the low fire setting on your modulating burner still produces too much steam for the system at low heating loads.
    Bburd
  • Acon12
    Definitely a possibility. I’ve run the manual fire rate adjustment in minimum and had it top out as well. Any suggestions to remedy?
  • bburd
    The remedy is beyond my experience I'm afraid, but others here will probably have a good idea.
    Bburd
  • retiredguy
    retiredguy Member Posts: 1,090
    That is a Gordon-Piatt burner that could be fired with gas or oil. You need to call a burner tech company and see if the low fire firing rate can be set a little lower. If not, just let it cycle on/off. Some of those units had pilot lighting problems which were always a nuisance.
  • ratio
    Are the two boilers identical? Clock the meter/check pump pressure at low fire to see if they're actually firing at the same rate. How are they connected together?