I have a low pressure Burnham 3 pass firetube stream boiler with a Gordon-Pratt 12S burner. I adjusted the modulating pressure control to modulate the boiler around 4 psi (with additive diff) with the operating control set a 6. I can see the boiler gets to low fire in the modulation, but the boiler still trips on operating pressure of 6 and begins another cycle. I would like to run longer cycles and have adjusted the mod pressure down at times to see if it holds a consistent pressure, but it continues to top out. Any idea why that is?
If the pressure is rising, you're making more steam than you're condensing. What application?0
I’m overseeing an old elementary school. 1920s build and 65,000 sq ft. There’s about 20 radiators throughout and I have a little over a dozen reheat boxes that heats air pushed into the classrooms. Theres a couple preheat coils if needed. The strange thing is, I have twin boilers, and my boiler 1 runs and modulates with little to no cycling. They share the same one pipe systemratio said:If the pressure is rising, you're making more steam than you're condensing. What application?0 -
It sounds like the low fire setting on your modulating burner still produces too much steam for the system at low heating loads.—
Bburd0 -
The remedy is beyond my experience I'm afraid, but others here will probably have a good idea.—
Bburd0 -
That is a Gordon-Piatt burner that could be fired with gas or oil. You need to call a burner tech company and see if the low fire firing rate can be set a little lower. If not, just let it cycle on/off. Some of those units had pilot lighting problems which were always a nuisance.0
Are the two boilers identical? Clock the meter/check pump pressure at low fire to see if they're actually firing at the same rate. How are they connected together?0