Settings for Vaporstat + Pressuretrol in series?
delcrossv
delcrossv Member Posts: 2,189
edited January 2024 in Strictly Steam
Old pressuretrol gave up the ghost after 60 years. Ordered a new vaporstat 0-16oz as the main control. 1 pipe system, well vented.
Just checking, initial values for a vaporstat should be say 10oz cut out out and 3-4 oz cut in? Then monkey with it? Going in Wednesday night and then it's due to get really cold so I just need ballpark so everything works.
I also got a A type pressuretrol (main is cut in, diff+main is cut out). Where do you recommend I set that? It's just the "safety" rather than the operating control. Lowest cut in is .5 psi on the case.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,417
    You can delete the P404 or wire in series . The vapor stat will get the exercise..
    Mad Dog_2
  • delcrossv
    I'm gonna wire in series. Suggestions for setting for the pressuretrol?
    109A_5 Member Posts: 3,696
    edited January 2024
    Hello @delcrossv,
    Those number sound reasonable, 10oz cut out out and 3-4 oz Cut-In, PA404A Cut_In is 0.5 PSI, Cut-Out 1.5, with the PA404A you could go slightly higher with the Cut-In, since some have trouble cutting back in at the minimum of 0.5 PSI, although the PA404A may never trip unless the Vaporstat fails.
    If your boiler is not oversized and well matched to the EDR you may not trip either device.
    delcrossv
  • delcrossv
    Just to make sure, this is the L408J1009 (break on rise). Correct?
  • delcrossv
    edited January 2024
    Cheezus. Previous tech wired the LWCO and pressuretrol IN PARALLEL! 🤬 1&2on the MM 61.
    I already got the new parts so I guess I can keep the old, old, old WR pressuretrol as a spare. 🙄
    CLamb
  • ChrisJ
    ChrisJ Member Posts: 17,162
    delcrossv said:
    Cheezus. Previous tech wired the LWCO and pressuretrol IN PARALLEL! 🤬 1&2on the MM 61. I already got the new parts so I guess I can keep the old, old, old WR pressuretrol as a spare. 🙄
    I think that's known as an OR Gate.   ;)
    Not very useful in such an applicable.
    delcrossv
  • delcrossv
    Ever have one of those days?
    Got them installed: Resideo 404 pressuretrol leaks from diaphragm, put in plug on tree and returning for a replacement
    1009 vaporstat has no working differential, no matter what I set is at, it cuts in at 6 oz. per the gauge. Out of the box there was no tension on the diff spring. Gonna return that one too for a replacement, but it does cut out at 13 oz so it's better than nothing.
    Replacements should be here Friday.
    Are all new controls this bad?
    Nuts.
  • delcrossv
    edited January 2024
    Replacements showed up today. Some futzing, but got a stable 11 oz cut out and a 3 oz cut in. Note, the markings on the vaporstat have no correspondence with reality.
    Just in time for design day this Sunday .
  • delcrossv
    -9 degrees, running at 3 oz, cycles on thermostat. Apts at 70 . :D