Settings for Vaporstat + Pressuretrol in series?

delcrossv
delcrossv Member Posts: 1,352
edited January 9 in Strictly Steam
Old pressuretrol gave up the ghost after 60 years. Ordered a new vaporstat 0-16oz as the main control. 1 pipe system, well vented.

Just checking, initial values for a vaporstat should be say 10oz cut out out and 3-4 oz cut in? Then monkey with it? Going in Wednesday night and then it's due to get really cold so I just need ballpark so everything works.

I also got a A type pressuretrol (main is cut in, diff+main is cut out). Where do you recommend I set that? It's just the "safety" rather than the operating control. Lowest cut in is .5 psi on the case.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    You can delete the P404 or wire in series . The vapor stat will get the exercise..

    There was an error rendering this rich post.

    Mad Dog_2
  • delcrossv
    delcrossv Member Posts: 1,352
    Big Ed_4 said:

    You can delete the P404 or wire in series . The vapor stat will get the exercise..

    I'm gonna wire in series. Suggestions for setting for the pressuretrol?
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • 109A_5
    109A_5 Member Posts: 1,683
    edited January 9
    Hello @delcrossv,
    Those number sound reasonable, 10oz cut out out and 3-4 oz Cut-In, PA404A Cut_In is 0.5 PSI, Cut-Out 1.5, with the PA404A you could go slightly higher with the Cut-In, since some have trouble cutting back in at the minimum of 0.5 PSI, although the PA404A may never trip unless the Vaporstat fails.

    If your boiler is not oversized and well matched to the EDR you may not trip either device.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,352
    Just to make sure, this is the L408J1009 (break on rise). Correct?
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • delcrossv
    delcrossv Member Posts: 1,352
    edited January 10
    Cheezus. Previous tech wired the LWCO and pressuretrol IN PARALLEL! 🤬 1&2on the MM 61.

    I already got the new parts so I guess I can keep the old, old, old WR pressuretrol as a spare. 🙄
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    CLamb
  • ChrisJ
    ChrisJ Member Posts: 16,317
    delcrossv said:
    Cheezus. Previous tech wired the LWCO and pressuretrol IN PARALLEL! 🤬 1&2on the MM 61. I already got the new parts so I guess I can keep the old, old, old WR pressuretrol as a spare. 🙄
    I think that's known as an OR Gate.   ;)

    Not very useful in such an applicable.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,352

    Ever have one of those days?


    Got them installed: Resideo 404 pressuretrol leaks from diaphragm, put in plug on tree and returning for a replacement

    1009 vaporstat has no working differential, no matter what I set is at, it cuts in at 6 oz. per the gauge. Out of the box there was no tension on the diff spring. Gonna return that one too for a replacement, but it does cut out at 13 oz so it's better than nothing.
    Replacements should be here Friday.

    Are all new controls this bad?

    Nuts.
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • delcrossv
    delcrossv Member Posts: 1,352
    edited January 13
    Replacements showed up today. Some futzing, but got a stable 11 oz cut out and a 3 oz cut in. Note, the markings on the vaporstat have no correspondence with reality. 

    Just in time for design day this Sunday .


    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    ethicalpaul
  • delcrossv
    delcrossv Member Posts: 1,352
    -9 degrees, running at 3 oz, cycles on thermostat. Apts at 70 . :D
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.