You need a short length of wire to “jump” across the R & W terminals of the zone in question.0
Ok think I found some spare wire that was marked 24V, so that means keep the R and W of the zone in question in place but add in a small U shaped jumper wire?0
Ok so I used the jumper and it turned on the red light on the SR506 for the zone in question, assume that means something up stream?0
This is what the inside of my Nest looks like
You have eliminated the thermostat and the thermostat wires from the circuit by your first “Jumper” test. Now you want to eliminate the thermostat. You do this by connecting the Red and the White wire at the thermostat. If you connect them together and the circulator works, then the wires are good and the thermostat is bad or programmed incorrectly,
If you connect them and the circulator does not work, then you have found the problem. It is in between the thermostat and the Taco SR relay. Perhaps in the air conditioning unit where both wires are connected together.
Just picking up where @pecmsg left off
Ok thanks so much @EdTheHeaterMan
i just connected them and the unit turned on but still no circulator activation / heat so perhaps next stop is going to check the unit in the attic. Will report back0 -
Checked the handler in the attic but not sure what I am looking for, attached some pics. I am wondering if during the renovation of my addition they accidentally cut a wire that ran off of the unit and alongside the wall where we put an addition in...grasping at straws at the moment
If I put the jumper in place on the Taco SR506 will that allow me to use the heat with the Nest controlling temps (e.g. turn on / off when it reaches set temps) or will it just run continuously until the jumper is removed?0 -
It would just run until you took the jumper off. But did you say that when you connected red and white at the thermostat that the unit turned on but the circulator didn't? But when you jumpered at the Taco the circulator did start? What, exactly, do you mean by "unit"?Br. Jamie, osb
I can see that you have a Hydro-Aire type system. your thermostat connects to the First Co. air handler. when there is a call for heat the fan will blow air thru the hot water coil.
The thermsota tis operating properly to turn on the heat. there is a part called a relay inside the air handler that is not connecting the call for heat to the circulator control.
Your problem is inside the First Co. air handler. Are you up for looking at wiring diagrams?Edward Young Retired
When I connected the red and white a the thermostat, the air handler turned on and cold air started blowing but the circulator and red light on the Taco did not turn on. When I jumpered the R & W on the Taco unit for the zone in question, the circulator turned on and the light turned red.Jamie Hall said:It would just run until you took the jumper off. But did you say that when you connected red and white at the thermostat that the unit turned on but the circulator didn't? But when you jumpered at the Taco the circulator did start? What, exactly, do you mean by "unit"?
By the process of elimination you have ruled out the thermostat connection to the First Company Air Handler. and you have eliminated the Taco SR zone control and boiler. the section in red is the problem area.
Will be watching the Eagles Game for the next few hours. I' check in later this eveningEdward Young Retired
Thanks Ed, at least I've now whittled it down based on your help. I think something was cut when they did the addition work (which was over the summer so we never tested the heat). I will reach out to my contractor tomorrow and see if he can have someone take a look.....I surmise the only cause here is something wrong with the wires running from the Air handler to the Taco controllerEdTheHeaterMan said:
Will be watching the Eagles Game for the next few hours. I' check in later this evening0 -
at the Nest ,
don't we need a jumper between RC and RH ?
or does Nest do that internally in the setup ?
Did this work before the Nest ?known to beat dead horses0 -
One Pipe System0 -
sorry, was watching my patriots try and play a football game. ed has you going in the right direction. id the hydroair being used as one zone or is it being zoned too?0
so your hydroair only feeds one bedroom?0
From your pics it looks like there are 4 takeoffs off of your hydroair unit so there must be 3 other locations not getting heat too.0
Yes, those are all just going into differing vents in my bedroom + maybe some in my closet and master bathroom - all not getting heat. I think perhaps there is something wrong with the specific wire that serves to communicate between the hydroair in my bedroom / bathroom / closet and the Taco controller downstairs?pedmec said:From your pics it looks like there are 4 takeoffs off of your hydroair unit so there must be 3 other locations not getting heat too.
must be a big bedroom for one system. if that's the case then, yes, looks like your 2 conductor from the air handler to the zone panel has been severed.0
To get some heat in the bedroom, You could jumper the TACO SR zone and use the thermostat to turn the fan on and off. You will be wasting some fuel but you will get heat thru the night until the repairs can be made.
You asked that before but without more info I could not say YES to that.
But now I can. YESEdward Young Retired
Awesome! Thankfully not that cold in the northeast and I will be able to get this all fixed ahead of the real winter. My contractor will handle since he / his subs did this during renovation when they were probably cleaning out old wires. I take it the solution is for the HVAC wire to just get re-run between my handler and my Taco?EdTheHeaterMan said:To get some heat in the bedroom, You could jumper the TACO SR zone and use the thermostat to turn the fan on and off. You will be wasting some fuel but you will get heat thru the night until the repairs can be made. You asked that before but without more info I could not say YES to that. But now I can. YES1 -
I believe you mean @pedmecEdTheHeaterMan said:You have eliminated the thermostat and the thermostat wires from the circuit by your first “Jumper” test. Now you want to eliminate the thermostat. You do this by connecting the Red and the White wire at the thermostat. If you connect them together and the circulator works, then the wires are good and the thermostat is bad or programmed incorrectly,
Just picking up where @pecmsg left off1 -
@pecmsg OOPS, honest mistake, knowing your passion for NEST products.
HVAC guy came and confirmed that I do indeed have a cut wire between the air handler and the relay switch. Thank you to all for leading me in the right direction. Next up: electrician to run a new wire0