Steam radiators turned on with thermostat below set point
Does that sound like a thermostat issue?
Well, something is asking the boiler to fire. It could be the thermostat. It could also be a short in the thermostat wiring -- or are there any other controls which can fire the boiler? Like an indirect hot water heater or an aquastat controlling the boiler for domestic hot water?Br. Jamie, osb
I agree with @JUGHNE and @Jamie Hall . Is the compress turned off or has it failed? Is there a tankless coil or outdoor reset control that could also fire the boiler?0
Is this an older thermostat? Will adjusting the heat anticipator help? Short of replacing the T-Stat?
It's been a while since I adjusted an anticipator with an amp probe meter.0 -
Show us a sampling of your various thermostats please.0
Going to try and reply to the all the comments here:
Yes - it is an older Honeywell...looks like this:
The air compressor system appears to functioning normally. It turns on as needed and hold about 13 psi steadily.
The system appeared to respond this morning when I turned down the set point but, I'm guessing based on what the other comments say is that it is likely the thermostat which needs replacing.0 -
@lawsonkline
With a mixture of electric and pneumatic controls it is almost impossible for anyone here to figure out what turns your boiler on and off.
If the boiler does not run all the time to maintain steam pressure, then for the pneumatic side you probably have a PE switch which is a pneumatically operated electric switch that will turn the boiler on. For the electric side if you have any steam zone valve, they would use the valve(s) end switch to operate the boiler probably used with some control relays as well.
Would need a lot more information to be able to help.1 -
Is the thermostat secure on the wall? Did it get tilted off level somehow?0
That is the old standby favorite thermostat of all time. The Honeywell T-87F Thermostat.lawsonkline said:Going to try and reply to the all the comments here:
It has a mercury switch inside and a heat anticipator.
As @mattmia says above. Make sure it is securely fastened to the wall. Has it been moved or hit recently?
At this point, it might be best to change the thermostat. That type ( now offered without the mercury switch) is not terribly expensive and might correct things for you. Why not give it a try?0 -
Here is another thought.lawsonkline said:I have steam radiator system with some rooms on old pneumatic thermostats and others on hand valves. The system worked properly when turned on a few weeks ago but, the other day all the radiators were hot even though the set point on the main thermostat was well below the room temp. That hasn't happened in the past so I'm guessing it's a tstat issue but wanted to ask before replacing it.
Pneumatic heating valves fail in the open position. If you have a main valve that has lost its air supply. Maybe the air tubing is leaking or disconnected. This could also cause the issue you are having.0 -
We would like to see your other tstats, the pneumatic ones and the controls at the compressor also.0
