Tankless coil mixer valve
stevel87125
Member Posts: 7
in Oil Heating
On a new install, with a tankless coil, I see no automatic mixing valve, but a manual gate valve.
With low and high limits set on 160 and 180 respectively, how is a safe DHW temperature regulated?
Thank you
Thank you
A Picture would help to verify...but that's temperature blending from 50 years ago! You need a Watts or Taco Domestic How water mixing valve....and a thermometer Guage in the mixed outlet is ideal. Mad Dog 🐕2
A 520 Caleffi is ideal for tankless and tankless coil. Fast responding and if it loses hot or cold, it shuts down.Bob "hot rod" Rohr
Living the hydronic dream1 -
There is no mixing valve. How is the DHW being maintained at a safe temperature?
It's not. The hand valve is old school, run the hot water and manually adjust the hand valve unitl its tempered down.stevel87125 said:There is no mixing valve. How is the DHW being maintained at a safe temperature?
Today 120°F is maximum for point of use.0
