Tekmar Radiant Controls
Greetings,
I have not stayed up to speed on Tekmar controls the last years and have a large job that needs to operate independently and also interface with a crestron system.
I find all their choices very confusing to navigate
This is a Radiant Heat only, 23 zones, 60 actuators.
Viessmann 280MBH boiler. Just need TT. No mixing, no 0-10V.
If it did not need to interface with Crestron, I'd simply use a series of Taco ZVC406EXP
Needs to interface with Crestron system
Can anyone point me to the components to make this happen in the world of Tekmar?
Thanks,
Jacob
  • Teemok
    Teemok Member, Email Confirmation Posts: 757
    edited October 2023
    This was done wirelessly with apps at the thermostat level on a recent project. Savant system. ZV control is as normal. I don't know how Crestron is supposed to interface. Third party Tstats to Crestron and Crestron to ZV seems silly today. Crestron senors and their app to control the ZVC via a switch makes some sense.
    hot_rod Member Posts: 26,599
    60 actuators? What type?
    somehow you will need enough transformer to power all those
    if they are low current draw helmet heads, 7 on a 40 VA transformer
    You may  still need relay boxes daisy chained together to get your 24v
    Then the Creston  interacts with the relay boxes
  • SoCal_Hydronics
    SoCal_Hydronics Member Posts: 11
    These are Helmet Heads. I believe on the last job I used their RS232 gateway for the low voltage contractor to control the TN2 stats. That job was more complicated with Jaga fancoils doing heating + Cooling. This is simple Floor Heat only -- boiler has all the reset functions etc. I just want make sure I understand which product to start with, then which products to add to achieve 23 zones. Also whether I need Tn2 or Tn4. I used a RIB 100VA Power supply.
  • Teemok
    Looks like a 482 with four 335's and 23- 532 t-stats. I Have not set this combo up so my experience is limited. You should be clear before ordering. DHW? I don't know if you want switch pumps with Tekmar so you may need a different zone manager. Careful with micro zoning, a buffer tank might be good to help with short cycles. Twin or big/small boiler pairs provides faster from cold warm ups, redundancy and a lower minimum firing rate.
  • SoCal_Hydronics
    Thanks. I do have a 40 gl buffer tank on the primary.
    Teemok
  • Zman
    Zman Member Posts: 7,611
    edited October 2023
    Why not just use Crestron t stats? https://www.crestron.com/Products/Featured-Solutions/Horizon-Thermostat, As @hot_rod mentioned, you will still have power issues for the Zv's. You can always use a zone controller zone for each valve and jump the t-stats together on the controller.
    Albert Einstein
  • Teemok
    Stand alone requirement. There's no zv power issues.