Oil line sucking air?
bruce_21
Member Posts: 246
in Oil Heating
My customer/neighbor's oil tank is full, but the burner fired once for a minute and a half and then shut down. The one-pipe oil line runs UP from the burner to the basement ceiling and across the basement 30-40 feet to the new oil tank and into the top of the tank, see the picture. There is just a plug in the bottom of the tank.
Can this be remedied by going to two-pipe?
Has the fuel filter been changed??0
Double check all the connections for being tight. It may have a connection which leaks a bit of air -- it wouldn't take much -- under vacuum, and an over the top piping arrangement like that is going to be very susceptible to that.Br. Jamie, osb
It would be better after checking for leaks to power purge it.
A tiger loop is a band aid in my opinion. It does not fix the underlying problem. If it was my job it would be two pipe.
Other opinions will differ.0 -
I agree with you Ed, I was just thinking that a 2 pipe system with a tiger loop and a combination check valve with vacuum gauge and Schraeder valve would be beneficial and simplify things.0
No tiger loop.
If all the fittings are 100% oil tight, then no air can get in. If air can't get in then why do you need a Tiger loop which is a deaerator? It's a basement tank.
Make the piping tight, no air leak the burner will run weather it is 1 pipe or 2 pipe.
I was taught 2 pipes when you lift oil and that's the way I am staying.2 -
I would take the supply off the Bottom , valve and filter . Single pipe over , no fittings and valve above oil level with a Tigerloop at the burner....
@bruce_21
Your picture seems to show compression nuts before the valve on the elbow. After the valve, it shows a flare fitting.
I have replaced many a compression nut with a flare fitting for this type of problem. Compression nuts on oil lines can, at times draw in air. (Crazy). But I have done it in the past and the air problem can go away.
Also. At that pumping/fuel unit to tank distance (30-40'from the tank?) You should have a two-pipe system fuel line set up similar to this picture.
- 119 Chimneys & Flues