Oil line sucking air?
bruce_21
Member Posts: 241
in Oil Heating
My customer/neighbor's oil tank is full, but the burner fired once for a minute and a half and then shut down. The one-pipe oil line runs UP from the burner to the basement ceiling and across the basement 30-40 feet to the new oil tank and into the top of the tank, see the picture. There is just a plug in the bottom of the tank.
Can this be remedied by going to two-pipe?
Can this be remedied by going to two-pipe?
0
Comments
-
Has the fuel filter been changed??0
-
Double check all the connections for being tight. It may have a connection which leaks a bit of air -- it wouldn't take much -- under vacuum, and an over the top piping arrangement like that is going to be very susceptible to that.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
It would be better after checking for leaks to power purge it.
A tiger loop is a band aid in my opinion. It does not fix the underlying problem. If it was my job it would be two pipe.
Other opinions will differ.0 -
I agree with you Ed, I was just thinking that a 2 pipe system with a tiger loop and a combination check valve with vacuum gauge and Schraeder valve would be beneficial and simplify things.0
-
No tiger loop.
If all the fittings are 100% oil tight, then no air can get in. If air can't get in then why do you need a Tiger loop which is a deaerator? It's a basement tank.
Make the piping tight, no air leak the burner will run weather it is 1 pipe or 2 pipe.
I was taught 2 pipes when you lift oil and that's the way I am staying.2 -
-
I would take the supply off the Bottom , valve and filter . Single pipe over , no fittings and valve above oil level with a Tigerloop at the burner....
There was an error rendering this rich post.
0 -
@bruce_21
Your picture seems to show compression nuts before the valve on the elbow. After the valve, it shows a flare fitting.
I have replaced many a compression nut with a flare fitting for this type of problem. Compression nuts on oil lines can, at times draw in air. (Crazy). But I have done it in the past and the air problem can go away.
Also. At that pumping/fuel unit to tank distance (30-40'from the tank?) You should have a two-pipe system fuel line set up similar to this picture.
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements