Swap positions of the Supply & Return?
SteamtoHotWater
Member Posts: 123
Originally, I had sketched my primary return on the left and the supply on the right because that's the way it was drawn in the manual. Well, in practice I'm running really short on space on the left of my wall. There's a minimum width on the supply side because of the zone valves. But I can make the return pipe widths really short. Is it okay for me to simply pipe the return to the right of my supply, or is something bad going to happen?
To me it seems like it shouldn't matter, but what do I know?
The water doesn't care...Br. Jamie, osb
Well if the water doesn't care, than neither do I.Jamie Hall said:The water doesn't care...
Just thought I should ask. Something really bad happens if you exceed 12" between the supply and return. So I thought something catastrophic might happen if I swap positions.
Yor low loss header takes care of the 12" as long as you have the connections on that right you are ok.0
The limitation for that 12" spacing is only at the "closely spaced tees" as shown in the manual. The piping itself can be a mile apart, as long as the tees are within 12" of each other (closer is better) for hydraulic separation. You are using a hydraulic separator in place of the closely spaced tees, so that can be disregarded entirely.0
Nice to see your plan come together
What is your load on each of your zones? Did you go with the 140k or 199k combi?0
