NPE-240 for baseboard heat?
josephny
Member Posts: 428
I have a small cottage (about 1000 sq ft) and I'm considering putting in hot water baseboard (with some panel).
Would a Navien NPE-240 (leaving aside the capacity question) be appropriate?
I've seen warnings about not using tankless as boilers.
Thank you!
Why wouldn't you get a boiler, since that's what you need? Here's a discussion of some small gas boilers that might be more suitable for your cottage:
https://forum.heatinghelp.com/discussion/165166/looking-for-the-smallest-btu-input-condensing-gas-boiler0 -
No, it wouldn’t be. It’s a water heater, not a boiler. It’s not designed, controlled or approved for space heating.
Your house probably needs less than 25k btus to heat it and that’s on the coldest night of the year. Why would you want to install something that’s almost 10 times that size? Even if it could be made functional, it would short cycle itself to death in a short time.
If you’re bent on doing this on the cheap, then use a gas fired tank water heater.Bob Boan
Thank you all!
I suspected as much, from my research and reading here and elsewhere.
The local heating guy is proposing to use this. He is a youngish guy but comes from old school oil and gas floor mounted boilers.
While the house is really just a small cottage, I am in Sullivan County, NY where it gets mighty cold.
And, if I'm doing this, I was thinking of getting a combi to eliminate the tankless water heater hanging in the attic.
A local dealer who I have dealt with before and has been very helpful in doing the work myself is an IBC dealer.
Does a propane combi from IBC make better sense for my need?
Thank you!0 -
Size your panel rads and bb to run at 120f supply. The will keep the combi condensing
A boiler around 110 - 120k would give you around 2 gpm of dhw. Probably plenty for a small cottage
Thise small combis turn down to around 8k. Much lower than a water heater or a small cast boilerBob "hot rod" Rohr
Living the hydronic dream1
- 120 Geothermal