High efficiency wall mount boiler diagram questions
The tube to the right of the boiler, is that a supply? Going where?
your loop cannot connect, cut it under the boiler and cap both ends like this drawing
now the boiler pump is injecting into a loop like the drawings I posted earlier
It us hard to tell with piped in front of one another and no labels or arrowsBob "hot rod" Rohr
hot_rod said:The tube to the right of the boiler, is that a supply? Going where?
It us hard to tell with piped in front of one another and no labels or arrows0 -
Again, a loop as you have will never flow anything to the zones. Path of least resistance and all that. You need to have a supply header and a return header, similar to what hot rod drew up. If you can cut the loop between the 2nd supply and 1st return and cap them both, then it should flow. No diagram anywhere shows a loop like you have, unless there are additional circs on each zone to pull from said loop, or a pressure differential bypass. You are using zone valves the way it looks, so there is nothing to create flow through the zones unless there is a disconnect between the last supply and first return. The circ is properly mounted now, sorry I did not realize that those were rotating flanges.0
GroundUp said:Again, a loop as you have will never flow anything to the zones. Path of least resistance and all that. You need to have a supply header and a return header, similar to what hot rod drew up. If you can cut the loop between the 2nd supply and 1st return and cap them both, then it should flow. No diagram anywhere shows a loop like you have, unless there are additional circs on each zone to pull from said loop, or a pressure differential bypass. You are using zone valves the way it looks, so there is nothing to create flow through the zones unless there is a disconnect between the last supply and first return. The circ is properly mounted now, sorry I did not realize that those were rotating flanges.0
I'm not sure of your plan? I'm not seeing that you are correcting the problem?
Can you draw it on paper before you cut and change?
The pipe just to the right of the gas line that goes vertical, is it a supply to a zone?Bob "hot rod" Rohr
hot_rod said:
I'm not sure of your plan? I'm not seeing that you are correcting the problem? Can you draw it on paper before you cut and change? The pipe just to the right of the gas line that goes vertical, is it a supply to a zone?0 -
But what is the tube going up left of that ball valve? it it is a supply, you valve location will not work.Bob "hot rod" Rohr
hot_rod said:But what is the tube going up left of that ball valve? it it is a supply, you valve location will not work.0
Your first pic at the beginning of this thread showed two supplies, red, 2 returns blue. What is the 3 rd return?Bob "hot rod" Rohr
If both the lines to the left of the valve you installed are returns and the 2 that are stacked on each other are supplies , you are good .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38330 -
hot_rod said:Your first pic at the beginning of this thread showed two supplies, red, 2 returns blue. What is the 3 rd return?
That looks much better. You should be good to go now, if you can get it purged properly0
GroundUp said:That looks much better. You should be good to go now, if you can get it purged properly0
Yeah , not so difficult . https://www.supplyhouse.com/Uponor-Wirsbo-A3031003-Three-Zone-Control-Module . Or this , https://www.tacocomfort.com/product/zone-valve-controls/ . Or Caleffi . Really not a challenge , because the last guy was a Buffoon does not mean you MUST follow suit .
732-751-1560
Did you guys see this picture of what was previously there? Am I safe to assume that line on the left hand side of the picture with the red handle gate valve is a return line? That is the line you see that is to the right of the new boiler now0
Look like they added some sort if control onto the zone valves, got a close upBob "hot rod" Rohr
hot_rod said:Look like they added some sort if control onto the zone valves, got a close up0
Maybe ed or someone recognizes what they attached to the end of the HW zone valves, or why?Bob "hot rod" Rohr
I looked back and saw that @GroundUp wanted the left hand tee rotated 90° counterclockwise. I don't agree. A tee is a tee.
Two btu per sq ft for degree difference for a slab1 -
A tee is not a tee. Water takes the path of least resistance, which is a crapshoot when the tee is bullheaded like that. The only way to achieve proper hydraulic separation in such a system is to have both tees in the same orientation with flow traveling through all 4 runs, which is the path of least resistance.I looked back and saw that @GroundUp wanted the left hand tee rotated 90° counterclockwise. I don't agree. A tee is a tee.
Also, he already rotated it.0 -
There is really no way around a bull head tee with primary secondary via closely spaced tees
And flow could be coming from two different directions on the run, into or out if the tee branch. At two different flow rates even.So a variable omni flow bull head teeBob "hot rod" Rohr
Am I safe to move on to wiring ?0
Looks good, nice solder work
Consider a relay box like this. Super simple to wire, thermal fused transformers in case you get something crossed upBob "hot rod" Rohr
I think the zone valve in question is a Honeywell V4083. I do not recognize the "extension": that allows for a bx connector. I do not think there is really anything special about the electrical side of the zone valves.0
Here is a close up of each valve. Should I just remove all the wires and start over? They are Honeywell0
Look like they were trying to use the zone valve end switch to switch 120V? Not exactly code approved
And they added an additional junction box over the low voltage connections?
Need to see where the other ends of all those wires ends up.
4 low voltage thermostat leads is all you need to operate that valve correctly, and safely.Bob "hot rod" Rohr
This use to be the other end. I cut both about 1 foot away from the valve so they don't go to anything now.0
I stand corrected. The wires may in fact be two different voltages. I am concerned that there may be 120 volts flowing to at least two of the terminals (screws). It appears that some of the wires are thin 18-22 gauge that we typically use for 24 volts. However, it also appears that there may be heavier/thicker wires that might be carrying 120 volts.
I suggest you test with a voltage meter before proceeding.0 -
That my have been a good idea back then to avoid the extra wiring for a relay. And it's been working all these years, so you can't fault them for it. Now's the time to upgrade to a proper zone valve control. Easy to wire, easy to troubleshoot if a thermostat or zone valve ever go bad.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Would be a shame to leave those ugly zone valves in there . Purchase some new ones and a proper zone valve relay like I linked or what Hot Rod linked . You'll be glad you did .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38331 -
Rich_49 said:Would be a shame to leave those ugly zone valves in there . Purchase some new ones and a proper zone valve relay like I linked or what Hot Rod linked . You'll be glad you did .0