LG Heat Pump Need Neutral?
josephny
Member Posts: 428
I had 3 LG heat pumps units installed (LUU18HHV, LUU24HHV and LYY48HHV) and I just noticed that the wiring to each unit includes 2 hots and a green ground. No neutral wire.
I opened the outdoor disconnect but not the wiring panel on the LG units.
I know enough to know that a ground does not take the place of (or serve the same purpose as) a neutral. Nonetheless, this is a single family house in a rural area and the grounds and neutral lines are all tied together in the breaker panel.
Is this okay?
Here's a pic:
(Don't know why a black and a red were used.)
1
If the equipment has no need of 120 volts -- which is actually rather common -- there's no need for a neutral. Black and red are the two colours normally used for hot lines. White would be a neutral and green ground. It would appear from the photo that somoone used a white wire for a hot, however. They should have marked it, but... that often gets overlooked.
I personally am not at all keen about the bare ground that close to the left hand break block, but... that's me.Br. Jamie, osb
Not familiar with the LYY part number, but the others are 208/230
when you hook up the control wire to the heads those are polarity sensitive and must be connected to the corresponding terminal on both the IDU and ODU0 -
Thank you all!
The unit says 208/230.
Other than the ground being too close, and the white instead of red used for a hot line to the unit, it sounds like I'm fine.
Thank you!!0
- 50 Industry Classes
