LG Heat Pump Need Neutral?
josephny
josephny Member Posts: 428
I had 3 LG heat pumps units installed (LUU18HHV, LUU24HHV and LYY48HHV) and I just noticed that the wiring to each unit includes 2 hots and a green ground. No neutral wire.
I opened the outdoor disconnect but not the wiring panel on the LG units.
I know enough to know that a ground does not take the place of (or serve the same purpose as) a neutral. Nonetheless, this is a single family house in a rural area and the grounds and neutral lines are all tied together in the breaker panel.
Is this okay?
Here's a pic:
(Don't know why a black and a red were used.)
Mad Dog_2
    Jamie Hall Member Posts: 27,328
    If the equipment has no need of 120 volts -- which is actually rather common -- there's no need for a neutral. Black and red are the two colours normally used for hot lines. White would be a neutral and green ground. It would appear from the photo that somoone used a white wire for a hot, however. They should have marked it, but... that often gets overlooked.
    I personally am not at all keen about the bare ground that close to the left hand break block, but... that's me.
    Rich_49
    mattmia2 Member Posts: 16,693
    edited August 2023
    If the equipment is 240v only the ratings plate will say 240vac, it it needs 120v so it needs a neutral it will say 120/240 vac.
    GGross
  • GGross
    GGross Member Posts: 1,877
    edited August 2023
    Not familiar with the LYY part number, but the others are 208/230
    when you hook up the control wire to the heads those are polarity sensitive and must be connected to the corresponding terminal on both the IDU and ODU
  • josephny
    Thank you all!
    The unit says 208/230.
    Other than the ground being too close, and the white instead of red used for a hot line to the unit, it sounds like I'm fine.
    Thank you!!