Prestige Triangle Tube 110 DHW open sensor error code E33? Help!
bushman432
Member Posts: 17
Hello, The title just about says it all. We have a 5 year old system that is displaying the E33 error code. Of course it's Saturday and I cant call in for service. Any ideas on a fix? We have hot water going to the heating and the DHW so far, but not sure if that is going to change, hopefully not. Thanks!
If the attached manual is the one for your boiler, that error is an open DHW temp sensor.
You could have a loose or bad sensor.
My guess is that you have a switch and someone accidentally changed the DHW setting in the boiler to sensor.
A picture of the water heater sensor well would help. It probably has a small diameter wire going into it"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Thank you so much Zman! I was trying to increase the temperature and inadvertently switched the unit to "sensor" mode. Once I moved control back to the "switch" everything started working again. Extra bonus, the hard copy manual that came with the unit didn't even contain this error, and your PDF manual does. We really appreciate your help.0
No problem. You can probably guess how I knew that was the issue. I'e done that...."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I just discovered the exact same problem, and I know absolutely nothing about this stuff. Can someone explain to me how to change the unit from "sensor" mode to "switch"??? Thanks.0
The instructions are in the manual posted in the above post^"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
- 15.8K Strictly Steam
