Hello - My aging Slant/Fin needs to be replaced. If they were still in biz, I would just drop in their latest Sentry. The boiler heats a 6-zone radiant floor heating installation. Model S-90 EDP, installed around 1999-2000.
Any practical experience with installing a replacement brand/model?
Thanks.
    hot_rod Member Posts: 26,467
    Is the boiler leaking? Tell us more about the system. A cast boiler with a mixing system for radiant?
    A mod con would be another good option if it is a low temperature system, around 130 or lower supply?
    kr51mattmia2
    Steamhead Member Posts: 18,180
    @kr51 , also has anyone done a heat-loss calculation on your house? That is the proper way to size a new hot-water boiler.
    Consulting
    kr51ethicalpaul
  • kr51
    It was leaking substantially as well as, over past several years, system would depressurize. I suspect an internal leak and due to the age of the unit and overall condition, have decided to replace it. This process would have been a lot simpler last year, of course.
    Temps where I'm at rarely get below 40 deg.
  • kr51
    I've never had that calc done. I live in a moderate temp zone. I would consider not even putting the system back in working order, but I don't have forced air or other heating system. Plus, the system does work and it seems straightforward to replace the boiler with the same/similiar unit.
    I went on eBay and noticed Sentry s-120 boilers for sale. I need to review install manuals but seems like could be a good replacement option.
    pecmsg Member Posts: 6,740
    If you’re adding that much water that’s why the boiler failed.
    Find the leak and fix it!
    ethicalpaul Member Posts: 8,054
    A heat loss calculation is straightforward as well and could inform you that your replacement could be smaller and therefore less expensive to purchase and will run more efficiently.
  • SummitMechanic
    SummitMechanic Member Posts: 25
    edited August 2023
    To answer your question, a Super Hot Saturn series boiler is a good replacement for a copper fin tube boiler, and they still meet federal regulations on efficiency. 135 is the lowest they go as far as BTU's, but that should not be a problem.
    Experienced Boiler Mechanic In Summit County, Colorado.
  • john123
    john123 Member Posts: 83
    edited August 2023
    @SummitMechanic: does anyone make a copper fin tube boiler now? and is a steel boiler better?
  • Jersey2
    Jersey2 Member Posts: 173
    How about a Burnham X-2?
    I'm not a plumber or hvac man and my thoughts in comments are purely for conversation.