finding Sq. foot of steam
plumb1pa
Member Posts: 10
I've got some old radiators that I have never seen this shape. Where can I go to get info for steam load?
That looks like a hot water system?0
Sorry, steam0
Bundy Standard radiator made by A.A. Griffing Iron Co in NY. They come in heights of 24", 30", 36", and 42" and have 1-4 rows of loops. https://archive.org/details/bundyradiatorsfo00aagrrich/page/20/mode/2up If you look at the base of each of those, I believe you can just make out the company name. Make sure you have the standard loop and not enlarged. It will impact the EDR. See this: https://archive.org/details/illustrated1890900aagr/page/68/mode/2up
Both of those have two rows of loops, the second white one you posted is 2 rows of 8 loops (2 x 8), so as an example if it's 36" tall with a standard loop then the EDR would be 48 sq. ft. (p. 22 in the first link).
Here's another catalog from 1885: https://archive.org/details/AAGriffingIronCo/page/n7/mode/2up1 -
A 2 pipe steam system with air vent on the rad?
Is there some kind of steam trap on the outlet?
What keeps the steam out of the return line?0 -
Two pipe air vent steam. An older system, but it works very well.JUGHNE said:A 2 pipe steam system with air vent on the rad?
And nothing keeps the steam out of the "return" -- the system is described in The Lost Art.Br. Jamie, osb
Thanks Jamie, I just had a brain skip firing on all cylinders.
I have read about this numerous times.0 -
- 50 Industry Classes
